Hello all
Replacing a switch at the top of the stairs. Switch does the bathroom light as shown in the picture. And also top of the stairs but has a switch at the bottom of the stairs too.
The old switch has com l1/l2 and com l1/l2 first part is com+l2 for the bathroom and com l1/l2 for the...
Problem : addition of a 4P 2 way knife switch and the main house 1st floor RCCB is tripped if the switch changes position.
The simplified and relevant wiring diagram is like this (before addition of a 4p switch):
meter -> main breaker -> RCCB (sub main breaker) for 1st floor -> 3p MCB -> 4P...
Hi
I am sitting my AM2S next week. I feel fine with all of it except the lighting section. it requires a 2 way and intermediate lighting circuit to be installed. but unsure how to tackle it whether to wire at the switch or to go the light first. not that sure on it.
greatly appreciate if...
Hi,
I'm new to the forum and working on a van conversion - I also dabble in guitar pedals!
I have a wall mounted LED controller hooked up to my down-lights. I'd like to be able to turn the circuit on/off at another location in the vehicle (i.e. to make a 2 way circuit). Is it possible to add...
Hi,
I know there are many ways to achieve this. I just wanted to know that the diagram I have drawn for this 2way switch would work. Just having neutrals at each point, for future smart switches. Thanks and merry crimbo
I have double/dual/2gang 2way switch to control two lights.
The scenerio
Room has two doors one light is 4ft fluorescent and other right is installed just outside the door as security light it is oval bulkhead light.
No matter which door i enter i want to turn/off the 2 lights independently of...
As a newcomer here firstly I would like to say Hello to everyone.
I currently have a outdoor socket at the bottom of the garden (40ft from house).
This is supplied (on a radial) on a 20amp RCBO from the CU in the Garage.
I would like to run low voltage garden lights from this socket.
So here...
Evening Evening!
currently have a situation where I have:
switch on loft landing (2way)
switch on 1st floor landing (2way)
which turn some down lights on/off on 1st floor
-SL from the lights is at switch on 1st floor........and 3core from here to loft lanidng
now customer ALSO wants a 3rd...
Any one come across a waterproof IP65 or similar replacement for a standard 2way switch in a 35mm recessed back box?
Ive been looking around but have come up blank.
Its a finished and tiled internal wall, and furniture makes its unacceotable to have the added depth of a surface IP switch.
Went to a job today, where the client had removed 3 halogen bulbs to install LEDs. When the light was turned off from one side it would make the bulbs flicker with switch off, but if it is switched from other side it was ok. I dissconnected 2way switch and if was working fine. There is a new cu...
Alright Chaps, I've a long corridor in an office block that I'm fitting some 360 PIR sensors to the lighting, I need the lights to come on all at once for all locations of the corridor but there is a blind spot so I'll need to fit 2 sensors... Is there a sensor out there that you can link...
I could do with keeping the range of switches the same.. Screwless flat plate toggle switch but can't find a 2gang intermediate toggle.
An ebay seller (291055653971) has a diagram configured with 2way only but I cant see how!
Alternatively if anyone knows a range that has a 2g intermediate in...
Good evening all
im in a bit of a pickle. I've wired 2way switching that controls 4 sets of lights from 4 different points. Basically 4g switch on each floor.
ive some how really confused myself. I'm having to change some of the modules as intermediate works out in different location for one...
Morning everybody, Im new to the forum so please be aware if I don't post in the correct protocol.
What I would like to know is can you use two PIR detectors at either end of a corridor as per a 2way switching set up as is now the case ?
I have recently changed the consumer unit on a clients house. I even carried out insulation resistance testing on the existing circuit prior to installation to prevent any problems later. All was well until the light in the stairwell was switched on and it tripped both RCD's! two circuits...
Hi All,
Wonder if anyone could throw some light on this one (forgive the pun)-
Was called out to sort problem with landing light which blows the bulb when switched on.. mcbs not tripping and lighting is not on an rcd protection.
visited and looked at switches, both 2-way 2 gang coupled with...
Right guys got a 2way intermediate sscenario the 3 switches need to be dimmers (the dimmers are the issue)and dimmable lamps in the fitting
anyone suggest a particular make lights are all spotlights 22 in total split in 4 zones so minimum load could be 30 watt
looking at the Kosnic route anyone...
Hi there, just wondering if it is possible to get a led remote dimmer with 2 way connections on the back to a pull switch. What i have got is 4 halers dimmable light fittings in a bathroom with two doors. Obviously the dimmer is on the outside of the bathroom and i have a pull switch at the...
hi, doing some work for client and they have asked for a fan to be 2 way switched, 1 switch in utility room and the other in the bathroom next door
my query - is 2 way switching for a fan the same wiring as 2 way lighting with a permanent feed going to the fan for a run on timer??
thanks