This is a 2/0 CU Feeder wire coming into the main subpanel on a 200A service. There are no nicks in the copper wire and from the front side everything looks good.
But upon further inspection, the tiniest bit of wire insulation is under the lug on the back side.
Does this pose any type of...
I am working on a RV Park and I have a question.
I plan on installing 4/0 quadraplex AL URD cable to 10 pedestals on a 200 amp circuit and downsizing the wire to 2/0 Quadraplex AL URD cable for the last 4 pedestals. I have calculated voltage drop and everything is below 4%. Table 310.16 says...
This is a solar tie in generating 22 amps max current, hence the 25a/2p breaker on the subpanel but is there any reason the breaker feeding the subpanel has to be an 80a/2p? Can it be a 50a/2p?
Attachments
IMG_0010.jpeg
514.6 KB · Views: 2
This is a solar tie in generating 22 amps max current, hence the 25a/2p breaker on the subpanel but is there any reason the breaker feeding the subpanel has to be an 80a/2p? Can it be a 50a/2p?
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the utility meter, terminating to a 200AMP Main Service Panel in a Quonset Hut (think large garage). Inside the main panel is a 60AMP breaker that feeds a...
I have 6-6-6 triplex overhead that I'm running to a detached garage. At the weatherhead at the garage I'm going to splice 8 guage thhn copper to run down to the sub panel (approx 5' max of 8 guage at both ends of the run). This feeder will be on a 50a breaker.
Does anyone see any issues with...
Hi
after some advice on this, had a job to look at which involved replacing some ev chargers that were already there, the current set up is they go back to a feeder pillar, the chargers connect into rcds all the current protection is in place however the rcds/Mcbs are clipped onto din rails...
On a commercial 200A TP&N supply, what rating would the substation feeder pillar fuses be? Would they typically also be 200A or a higher rating?
Source URL: Electrical Forum - https://www.electriciansforums.net/forums/electrical-forum.15/
Hey there everyone,
I'm currently an EE student doing my 4th year project. As part of my project, I am carrying out a literature review into the design rules DNOs apply to their LV distribution networks.
I am trying to built up a reasonable understanding into how these networks are laid out...
Heres one for you automation gurus.
I'm looking to control the speed of a rotary feeder or conveyor that feeds a hammer mill on a farm. In order to achieve maximum efficiency the feeder needs to be regulated via the load of the hammer mill. The 55Kw motor on the hammer will be started using a...
Hi,
We have a control panel that has a vsd, plc and motor anti condensation heater. For a preliminary cable calculation for the control panel feeder cable and its associated protection, would we just total up the individual loads to arrive at an approximation and use this to size the feeder...
Hi Guys,
I am new here and would like you have your expert advice.
So I have a dwelling with 4 floors - basement, ground, first floor and roof and I was going to make 2 DBs, one in the ground floor and in the first floor.
Ground floor DB will cover basement and ground floor.
First Floor DB...
Hi.I've got a couple of queries regarding feeder pillars on a car park I an working at.
There are 3 pillars.All are metal.No 1 is supplied by 70mm 4 core xlpe swa.3 phase and neutral.cpc/bond is the swa.
No 2 is 25mm 4 core. And No 3 is 70mm 4 core. No 2 & 3 pillars also have water supply in a...
Dear all,
We have 460V MCC panel for existing pumps in our plant. We need to give supply to new 380V rated pumps in the same panel. There is space available in the panels(Out of 9, one panel almost free). So please suggest is it possible to make the arrangement for MCC feeders in the same...
We have a control panel that has a few fan motors (3phase) and two heaters ( 3 phase) and single phase loads to valve actuators. My question is regarding the sizing of the feeder cable to this control panel. Do we work out all the currents individually and then add them and treat this as a "lump...
Hi, could some one please explain to me the point at which the feeder stops and becomes a branch on the attached drawing. This is really bugging me and if I had hair it would all be ripped out by now and I am struggling to under stand. Anyone's help would be most appreciated.
Thanks in advance
Hello after abit of advice on adding a automatic start to my granddads pig feeding system,
when I installed it 8 years ago it was wired with a sensor on last feeder so when it was full it turned off and need start button pressing on the night.
has any one put a auto start system in ? do I need...
Anyone have any ideas for clearing concrete out of a 3" pvc conduit? We've tried muuratic acid but it evaporated after a few days and the obstruction is still there. To make matters worse..these guys pulled a rope through with a rag attached to it and it snapped...so now the obstruction which i...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc