phantom

phantom

  1. C

    How do I get rid of phantom voltage on LED lights feed.

    Have switched a light fitting from incandescent to LEDS. The LEDs continue to glow slightly after switching them off. The fitting is switched 240V live wires and there is a AC 5.1V induced phantom voltage. Little or no AC current. How do I get rid of the phantom voltage. A 4uF 400VAC cap across...
  2. M

    Megger 1533 showing phantom voltages on Ir and Impedance

    Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance tripping, this bits not important. Got my megger out, which has worked perfectly up until now, it doesnt have a test cert, but I'm not fully qualified and...
  3. T

    “Phantom” Short on radial circuit

    Hi, I’ve been recently working on a living trailer for a friend, when they have the supplies connected (240VAC 16A) they have nuisance tripping on the RCD. I’ve traced through and found an outside waterproof socket to be at fault, short circuit between live and earth. Removed the socket and...
  4. Lucien Nunes

    What's your definition of 'ghost voltage' ?

    I don't like the term 'ghost voltage' a.k.a. 'phantom voltage*' much, not least because it's rather loosely defined and probably means different things to different people. I also suspect that quite a few people use the term without really understanding what it is they are referring to. My...
  5. Electron

    Phantom EICR story...

    NICEIC don't cover me for EICRs as I am just a Domestic Electrician, not a Qualified Supervisor. So, I don't do many. However, a customer, who owns a HMO, needed one doing in a hurry for his Council Licence. Before I visited the property, I collected the last two EICRs and was surprised to see...
  6. Gavin John Hyde

    The phantom doorbell!.......

    Called to a small job this morning, woman in her mid 40's says her doorbell is not working properly... says it keeps going off but nobody is at the door as she can see the front door from her kitchen window. So I arrive and check it over. The switch is in good order and the wires go all way...
  7. HappyHippyDad

    Odd request regarding phantom voltage!

    Afternoon all... I would like to experience phantom voltage!! Is there any way I can reproduce it so that I can test it? I know this might sound a little silly, and I realise my new Drummond test lamp would simply not light up if it is phantom voltage, but I would just like to see it for...
  8. S

    Phantom Cooling Fan on Double Oven

    Hi all. Has anyone encountered a double oven cooling fan being turned on by the use of an electric whisk on the same circuit? Sounds bizarre I know but have just discovered the use of the whisk alone turns it on, without the oven even being used beforehand. Could some sort of high frequency...
  9. T

    The case of the phantom neutral.

    Hello, I have a lighting circuit that works with no neutral. I have removed all the neutrals from the board incase it was a shared neutral, and even went so far as to take the neutral and earth tails out and then turned on the MCB with just that light circuit and it works... Does anyone...