  1. KeenPensioner

    110 V between L and CPC

    I am in training and decided to do some dead tests using my second hand Fluke MFT 1653B on an upstairs ring. I did the tests at a socket rather than at the CU. Results end to end L - L 0.74 ohms, end to end N-N 0.76 ohms, end to end cpc >2000 ohms. I checked all the sockets on the ring and...
  2. D

    Final Ring Test during EICR

    Guys non domestic stuff here but is it true that you don't carry out ring final tests on EICR. Or is it that you don't have to and done do it as a matter of course anyway or do you charge extra for doing stuff not needed. I'm of the opinion of its not much extra to do it then I'll just do it...
  3. M

    High ring test results at socket outlets

    Hi, I was wondering if you guys can help with some errant test results. I'm testing a ring and i get L-L = 0.41 N-N = 0.40 E-E = 0.63 Great Figure 8 L-E = 1.0 ohms. Still good Figure 8 at each socket varies from 0.8 ohms to 1.1 ohms (I was expecting much lower)> Oddly Zs = 0.23 (which is...
  4. B

    r1 r2 rn ring test problems

    Hi all Im new to this site so bare with me if im in the wrong place, Your help would be very much appreciated, I have a ring main in a house and im testing r1 r2 rn, I get 0.48 ohms on r1 0.48 ohms on rn but also get 0.48 ohms on earths, which is wrong as it should be 1.67 times that of r1 and...
  5. S

    ring test

    Hi Guys, One of loads of questions, In A Brian scaddan book ive got it says, if you do the figure of eight, i.e link N-P at the c.u for instance ,then go in each socket on the ring and test between N-P, if you get a nil reading its either a open circuit or a reverse ploarity between N-E or...
  6. D

    0.00 on earth ring test?

    Trying to get my head around this doing r1 rn r2 test on a ring circuit today in metal conduit ran in singles, the r1 and rn where fine but when I came to the the r2 tester kept on recording 0.00 why little confused or is it obvious thanks in advance.
  7. C

    Ring test

    How do u do a test on your ring,

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top