  1. J

    Will the test meter over or under read the utility meter?

    Good day The following table shows the results of 3 current transformers (50A/5A, Class 0.5%) connected to a 3P-4Wire Digital Energy meter. (Performed at the meter manufacturer's workshop). It is observed that at Unity PF, the meter readings for current are a close match to the supplied test...
  2. M

    EICR test failed due to no RCD on smoke detector, lighting, door bell, security alarm

    Hi, I recently did an EICR test on my flat built in 2008. The engineer was in my flat for less than 10 mins, he was asking me irrelevant questions as in whether I am renting and that is interested to rent. In the end he said everything looks fine and will get the report in 24 hours. The report...
  3. mbu2ns

    EICR - RCD Wont trip on test button

    Hi all Still got a hangover from saturday but im struggling with one 🤣 EICR, everything tests ok until i press the button on the RCD and it doesnt trip. Tried 2 spare RCDs same thing. When i disconnect the sockets Neutral from the busbar it then works. Type AC 30ma 80A RCD What am I...
  4. P

    Difference between 250v/500v insulation resistance and 15ma/200ma continuity test?

    Hi I hope everyone is all well. I’ve built a rig at home on some ply to do some testing and fault finding to prepare for my exam and just learn in general… I put 100v then 250v through L & N through a B22 led lamp and also the spur neon to see what reading I would get. They were both the same...
  5. T

    R2 test without removing cover

    Hi all when performing an r2 test prior to commencing an EFLI test would it be acceptable if the board was made from metal of course to test from the point to the outside of the board rather than to the earth bar? Just for when you are working with large 3phase boards full of cables.
  6. L

    RCD test button

    Hi, can anything else cause a RCD test button to fail, besides a faulty RCD.
  7. S

    Test equipment for commissioning

    Hey guys What test equipment is the quickest and easiest to use when commissioning a system at the end of the job to get all required test results
  8. P

    What exactly happens during an RCD test? (Methods 1 & 2)

    Sorry this is a bit of a long read but I’d be extremely grateful if someone can help me understand RCDs and testing methods of them. I know RCD test applies a fault current but in what way? I understand how continuity/IR and the other test work so it helps me know what to do, what’s going on...
  9. T

    Extraneous conductive part test

    Hi all, im aware of the test needed to be done when trying to find out if a metallic object is an extraneous conductive part but for example, if you had a copper water supply system in a house that is fed with a plastic incomer pipe out the ground you will always receive a low resistance reading...
  10. P

    Max Zs values at different ambient test temperatures

    Hi guys, I'm currently revising for my 2391 and kind of confused on the temperature factors for the Zs values The BBB give Max Zs which are 100% values with a max operating temperature of 70c. The OSG and GN3 give values to 80% which are when tested at ambient temp of 10c according to page 146...
  11. M

    DIY solar — looking for PV array test report

    I did a DIY solar install without appreciating the need for building regs. Yep that was daft, but here we are. Hopefully will get the structural side sorted out. On the electrical side, building control are asking for an 'electrical certificate/report regarding the electrical installation and...
  12. N

    Why does a fridge freezer fail an insulation Pat test?

    Hi, I am getting a reading of 0.00MOhm I've never had this before, it's not tripping the rcd. I was wondering if it may be damp but can't see anything obvious. Any ideas please? It's not very old.
  13. J

    Insulation resistance test readings.

    Had an interesting one today, ring circuit blown the Mcb in a kitchen apparently a few times over last day or so. It has blown once when nothing was really in use in kitchen so kind of ruling out overload. When turned up and turned it back on it held for maybe 5 minutes before blowing again…...
  14. T

    Minor works certificate - Ze Test

    Hi on the minor works certificate it asks for Ze, so any time i install an addition to a circuit lets say, i then have to isolate the whole system disconnect the main earth and test each time? Is there anything that permits the test be completed without having to disconnect main earth? Thanks
  15. T

    NICEIC Test Sheets

    Hi , I have recently joined NICEIC and i am wondering if anyone can help me regarding recording the info on EICRs etc onsite on an ipad. I want my guys to fill out the test sheets onsite, on the app. However some sites you can't get internet and NICEIC say that they need this to fill out the...
  16. L

    UK The RCD test button on my tester trips the wall sockets

    We recently moved house (May 2024). The property is old (some >250 years), quite large with different outbuildings/extensions. From time to time the main power will trip (sockets not lighting). So I got out my cheap socket tester and all's well on various outlets, until that is I press the RCD...
  17. littlespark

    Adding test switch to emergency lighting

    I’m at the funeral directors clients at the moment testing their EM lights. Only the newer lights I put in have a test switch fitted. I’ll be recommending addition lights in the WC and staff rooms. Pitch dark in there. There are 2 other EM lights above exit doors… they have been replaced in...
  18. B

    EV chargers that I need to test on a commercial property

    Hi, just a quick question I haven't seen asked before. I have a number of chargers that I need to test on a commercial property. To begin, I have to download an app and create a profile and pay some money to my account in order for the EV charger to start releasing power so I can conduct my...
  19. J

    SECTT test

    Hi I’m taking my SECTT test in a few weeks, just wondering what it actually consists of? What to study and research as I can’t find anything online
  20. D

    Two Pages for circuit details and test results

    Why is there now two pages, one for "GENERIC SCHEDULE OF CIRCUIT DETAILS" and one for "GENERIC SCHEDULE OF TEST RESULTS" before it was all on the same page GENERIC SCHEDULE OF TEST RESULTS", which had "CIRCUIT DETAILS", on it, this means writing the cicuits twice?