  1. Rahi99

    What is wrong with bonding plastic water pipes and plastic gas pipes ?

    I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be in wrong if I have earthed the plastic gas pipes ? Can someone point me in right direction in on site guide if it’s wrong and why it’s wrong ?
  2. S

    Main water bond? Stop cock metal but plastic afterwards.

    Is there still a requirement to bond the main water if everything after the stop cock is plastic? Cheers
  3. N

    Do I need to upgrade gas and water bond for EICR?

    Do I need to upgrade the gas and water bond and upgrade main earth to pass the EICR?
  4. A

    Max water bond resistance

    Hi all so I have a situation where a client is moving and they want the db changed for selling. Db change is easy enough as is running a bond to gas which is currently missing. The only issue is that the last eicr said that the water wasn't bonded. It would involve major works (tiled floors and...
  5. J

    No Water bond

    Installed a cooker circuit on a fairly new house, found a 16 mm main earth and 10mm bond to Gas pipe. No water bond, there is a blue plastic water pipe entering house to stop cock and then copper pipe, lots of internal plastic pipe. Boiler has copper pipe with no cross bonding. The consumer unit...
  6. C

    Water bond, Insulated Section.

    Afternoon Gents, Came across a nice scenario today. Water pipe comes from the street, into the kitchen through a concrete floor. 100mm of copper behind a kickboard where it comes through the concrete 300ish mm of Plastic Pipe, 100mm of copper then stop tap. 90 percent of the installation is...
  7. N

    Water bond under carpet/furniture

    I am going to quote for a job (new circuit). Problem is the 10mm water bond is under the living room carpet/furniture as there is no stopcock in the house. I know it's within 600mm of the incoming water pIpe because I connected it there many years ago. I did a quick wander lead test from the...
  8. T

    Water Bond size on outbuilding

    Evening all. Bit of an odd one this and I just wanted to run it past bigger brains than mine to make sure I'm not missing something obvious. A brand new PME supply is being brought across to a field which has got 3 outbuildings, all of which need lights and a couple of sockets. The supply...
  9. 9

    main water bond new house

    Hi guys Just bought a new house and was having a look at the niceic test sheet. Main water bond is n/a So checked it out. Water not bonded. 400mm of copper comes out main stop cock and rest of house is plastic push fit. However hot and cold out boiler is copper around 1.5m again rest push...
  10. E

    Gas and water bond.

    House I'm working on has water and gas bonded on same 10 mm green and yellow cable. It loops from the water to the gas. Is this acceptable or a code 3?
  11. G

    main protective water bond??

    Hi. Jst on with a rewire at the mo. Did main incoming service bonds and now found that next doors water stop tap is in the cellar with about 3 meters of copper pipe in the property. U think this should be treated as a main protective bond? A supplementary bond? Or none at all? Thanks
  12. E

    gas and water bond, can i use 1 x 10mm cable?

    scenario is i have a consumer unit at one end of the house, and at the other end (20m away going the route i'm taking which is around the outside of the house) is the water stop cock and 200mm away from that is the incoming gas. so i was planning on using 1 x 10mm to save on cable, i thought...
  13. R

    Water bond?

    If a property is full of PVC push fit fittings on the copper plumbing and only about a meter and half underground before entering the house because before that it's PVC again, what is the bonding requirements?
  14. S

    pir code for undersizes water bond

    hi .doing a test on a complex where the tails are 25mm ..main bond 16mm ..but the cable bonding main water is only 6mm..think the tails have been upgraded from original but not water bond (not a easy run) .there are 30 flats in complex ..what pir code would i put fo this
  15. W

    Water bond

    Just been to price for a new cu, water bond cables is ridiculously short , not a chance ill get it direct into the new CU's earth bar? In terms of not breaking continuity , how can i get around this,obviously i dont want to be extending in a choccy block!
  16. B

    10 mm water bond ?

    I need to upgrade the bonding on a current installation but am having a problem locating exactly where to bond to. The consumer is in the cellar and so is the stop tap, however at some time in the past the pipe from the stop tap has been replaced with plastic, run across the wall and then...
  17. G

    no water bond, code query

    Doing a periodic at a primary school and am unable to locate where the mains water is isolated from, the earth bar doesnt account for a bond to the water as ive found where all the other go. Ive been told in the past no bond is a 1, but in this case i cant find where it is isolated so a 2 or 3...
  18. ste mac

    Water bond to earth electrode.

    On a domestic job today and came across an unusual bonding setup. The main house is TNC-S, supply to remote home office via SWA cable. The remote building has an oil fired boiler and the copper pipe work has a 10mm bond cable going out through the external wall to an earth electrode. The...
  19. A

    Main water bond. Regs on domestic smoke alarms.

    I'm doing a new build where the main water is run in plastic pipe. Is there a need for a main bond and if so where would the connection be? What are the regs on smoke detectors in a new build. I am doing a five bedroom detached house. All the rooms are big in size. The architect has a smoke...
  20. W

    main water bond to plasic pipes with metal pipes visable

    can any one help i have to do a peroidic inspection on new property aprox 1 year old wired with a 17th mains the main gas bond is in place but the water bond is not. the incomnig pipe is palstic and then it changes to a metal stopcok and then to copper the copper then goes into the wall. it is...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top