waverider
I am using 16 x 245w REC panels and a 3.6 Fronius inverter.
Max PPT voltage for the Fronius is 700V and the voc for the panels is 37.2V (x 16 = 595.2V)
So no problem to have it on 1 string.
Orientation and pitch exactly the same for all panels,
Min PPT 350V (8 x 37.2V = 297.6V). Does this mean I cant do it on 2 Strings?
I usually use Aurora Powerone and split it in 2 but can't get any.
Any suggestions as what would be best would be appreciated.
Thanks