10.5kW Shower Cable Size | on ElectriciansForums
Discuss 10.5kW Shower Cable Size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
N
Noob2013
Hi all,
Would a 10.5kW Shower require 10mm or 16mm twin and earth?
I've been doing cable calculations at college and im not 100%.
Cable Length = 20m
Protective Device = 50A
Wiring method = Above plasterboard ceiling not exceeding 100mm insulation
I belive 10mm is sufficient but my calcs are indicating 16mm which I've never heard of for a shower circuit.
Much appreciated
Can you include your cable calculations, it would be more helpful if you could.
As Pete says, please offer up how you come to your answer, then the guys will help you out.
I did 10500 Ă· 230 = 45.6 A
Then I used;
In
Ca Cg Ci Cf
50
1.0 x 1.0 x 0.78 x 1
= 50 Ă· 0.78 = 64.1 A
Table 4D5 shows 10mm can carry 45A with this wiring method.
I've now confused myself because that table shows 2.5mm can only carry 21 A
:S
Its due to the factors.
By dividing IN by 0.78 you are effectively sizing a cable that will handle a load 20% bigger due to the insulation FACTOR. Ci
In other words, ...DON'T run the cables surrounded by insulation material, either clip them on top of the loft joists or at the top of the sides of joists. It's not rocket science when all said and done!!
Hi all,
Cable Length = 20m
Much appreciated
Just to throw a spanner in the works, a 6mm cable will be fine for a 10.5kW shower if no derating factors apply, such as insulation or ambient temperature.
Just goes to show you how running cables in insulation is a bad idea!
If you need to run a new cable I would give the customer the price for 6mm and the "upgrade" to 10mm and let them decide. The upgrade isn't much!
Hi all,
Cable Length = 20m
Much appreciated
Seeing as you are an apprentice, i advise gaining access to the trainee section mate.
I am sure you will find it very useful for future questions. :)
apprentice?right. then the answer is to use 1.5mm cable so you can observe and study overload effects on cable .
Reply to 10.5kW Shower Cable Size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...