Hi all.. I was hoping for some advice please on installing a 10.8kw shower. I would like to know what amp fuse i need also would 10mm cable be satisfactory??... I have tried looking this up on other sites but everyone seems to say something different so i thought u guys would be my best bet...
Thankyou...
kind regards A-jay
 
Hi A-Jay
You will need to carry out a cable design calculation, and if you don't know how to do this you should question if your competent enough to carry out the works as this is one of the most basic of questions any electrician would be able to do,
Any way sorry if i sound harsh, i will how ever give you the basics

First work out the design current 10800/230 = 46.96A
Then select fuse size this will need to be a 50A, i assume you will use an MCB/RCBO?
Then you need to know if the cable is going to be affected by any other influences, Ambient temperature, if its going to be installed in thermal insulation and if its going to be grouped with other circuits.
This will all affect the current capacity of the cable lets assume you have no influences and the cable is clipped direct to a wooden surface Table 4D2A on page 276 ref method C 10mm T+E can take 63A

So in short the answer the answer to your question is 50A MCB and 10mm T+E but be warned you need to consider all the influences, and know how to check the voltage drop at the end

Hope this steers you in the right direction

Regards

AJ
 
Hi...Impressed with your quick resonse!!!
[ElectriciansForums.net] 10.8kw shower installation


I will need to run a 5 metre cable straight from fuse box through loft down to shower channelling wall.
 
Hi.. an electrician called out and told me i needed to run a 16mm T&E cable for this shower and told me to consider a 9kw shower lol

excellent thankyou.. Any idea where i can get a 50 amp fuse square D type QOE as i have also been told these are now obsolete
 
Last edited by a moderator:
Once the cable is fully derated taking into acct all external influences then maybe 16mm cable is whats required. Have you got a consumer unit or a fusebox (BS3036) fuses with fusewire, if so thats why 16mm cable is required as x 0.725 derating for BS3036. Also cant wire direct to shower need an isolator switch first

cheers
 

Reply to 10.8kw shower installation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
529
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
916

Similar threads

Hi, i am wondering if anyone has any experience with a 7.5-8kw shower that has a pump or some sort of boost internally fitted? Working at a hotel...
Replies
0
Views
272
C
  • Article
Tiling inside a shower Hi, first timers here... I am tiling my bathrooms and prefer the look & neatness of tiling inside the glass shower screen...
Replies
0
Views
220
Charlotte Livingstone
C

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top