We've got a customer who is losing 10% from the inverter to the generation meter and I can't for the life of me think why? The cable is 4mm and runs 20m, we're going to upgrade that to 6mm which will reduce the loss a bit but where is the rest going?

Any ideas??
 
my first thought would be a misreading rather than an actual loss. Doubt you've done it but I'd expect to see something like that if the meter was wired the wrong way round and then sorted out a bit later. Never heard of it by that much, but maybe the inverter reading is off? Or even the gen meter.
 
How many amps?
Perhaps a bad connection? Any of the connections getting warm?
In rough terms, 16A on 4mm2 gives a 3V drop so about 50W, so the 4mm2 is just about OK
Regards
Bruce
 
We've got a customer who is losing 10% from the inverter to the generation meter and I can't for the life of me think why? The cable is 4mm and runs 20m, we're going to upgrade that to 6mm which will reduce the loss a bit but where is the rest going?

Any ideas??

We had a faulty Elster 100A.

We changed eveything we could think of after Elster telling us they never go wrong. SMA were even prepaired to swap out the 4000TL inverter. We swapped out the meter and all was well.

Ours was loosing around 10-15% also. We now tell every customer to check to ensure there inverter and meter tally. Our general experiance with good set ups is that the inverter reads slightly less than the generation meter.
 
Last edited by a moderator:
We had a faulty Elster 100A.

We changed eveything we could think of after Elster telling us they never go wrong. SMA were even prepaired to swap out the 4000TL inverter. We swapped out the meter and all was well.

Ours was loosing around 10-15% also. We now tell every customer to check to ensure there inverter and meter tally. Our general experiance with good set ups is that the inverter reads slightly less than the generation meter.

What did you do about the MCS certificate and the Fit application? This is an install from 6 months ago and the customer has just checked the reading on the inverter with the Elster this week - it's 200 kwh out ....
 

Reply to 10% ac loss - what am I missing? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top