10 amp mcb ok for a single lighting circuit? | on ElectriciansForums

Discuss 10 amp mcb ok for a single lighting circuit? in the Talk Electrician area at ElectriciansForums.net

S

Simon_

My in laws house has a single lighting circuit for the whole house and the consumer unit is being updated. The lighting circuit has downlighters in the bathroom and kitchen. As well as the the RCD protection that's obviously needed would a 10a mcb be best for the circuit while a rewire is not an option at the moment.
 
As a rough quide, most people rate individual lamp holders at 100W, so a typical 3 bed semi will have about 9 or 10 lamps which will be about 900 or 1000W.
So your looking at a maximum load up to about 4.5A. Obviously sometimes there are multi-lamp fittings, and sometimes there are spot lights in kitchens and bathrooms, which wil increase the calculated load.
 
Doing the IR test is going to be a pain as there is quite a few downlighters on the circuit with transformers. Disconnecting them would be very time consuming. Any suggestions other than disconnecting them? Could I do L,N to E test and put notes in the limitations box on the cert after testing?
 
Remember the MCB size is protecting the cable and not the appliance!!!!

At the design stage, you should determine the load requirements of that circuit, then select the cable as required. There is no law saying you have to use 1.0/1.5 for lights and 2.5 for rings. You could design your lighting system and use a 10mm cable with a 40A MCB if you want (you may have trouble terminating the connections though :teeth_smile:)

As the circuit is existing, find out what size cable has been used, method of installation etc then select your MCB from this information. If after calculating the load demand for the circuit, you find the MCB will not be big enough, then it's time to run another circuit.
 
Will do mate. The main earthing needs upgrading when the CCU is changed. Bonding is fine though.

As you are upgrading the CCU then really the Zs of an existing circuit that can not meet the disconnection times for basic protection as in reg 411.3.2.1 then additional protection by an RCD with the characteristics of reg 415.1 can be used and therefore the Zs value of 1667ohm can be used from Table 41.5
 

Reply to 10 amp mcb ok for a single lighting circuit? in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
646
By code the washing machine needs its own 20 amp single pole GFCI circuit, the dryer needs a 30 amp double pole breaker and using # 10 wire. Your...
Replies
1
Views
706
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
1K
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks