My in laws house has a single lighting circuit for the whole house and the consumer unit is being updated. The lighting circuit has downlighters in the bathroom and kitchen. As well as the the RCD protection that's obviously needed would a 10a mcb be best for the circuit while a rewire is not an option at the moment.
 
As a rough quide, most people rate individual lamp holders at 100W, so a typical 3 bed semi will have about 9 or 10 lamps which will be about 900 or 1000W.
So your looking at a maximum load up to about 4.5A. Obviously sometimes there are multi-lamp fittings, and sometimes there are spot lights in kitchens and bathrooms, which wil increase the calculated load.
 
Doing the IR test is going to be a pain as there is quite a few downlighters on the circuit with transformers. Disconnecting them would be very time consuming. Any suggestions other than disconnecting them? Could I do L,N to E test and put notes in the limitations box on the cert after testing?
 
Remember the MCB size is protecting the cable and not the appliance!!!!

At the design stage, you should determine the load requirements of that circuit, then select the cable as required. There is no law saying you have to use 1.0/1.5 for lights and 2.5 for rings. You could design your lighting system and use a 10mm cable with a 40A MCB if you want (you may have trouble terminating the connections though :teeth_smile:)

As the circuit is existing, find out what size cable has been used, method of installation etc then select your MCB from this information. If after calculating the load demand for the circuit, you find the MCB will not be big enough, then it's time to run another circuit.
 
Will do mate. The main earthing needs upgrading when the CCU is changed. Bonding is fine though.

As you are upgrading the CCU then really the Zs of an existing circuit that can not meet the disconnection times for basic protection as in reg 411.3.2.1 then additional protection by an RCD with the characteristics of reg 415.1 can be used and therefore the Zs value of 1667ohm can be used from Table 41.5
 

Reply to 10 amp mcb ok for a single lighting circuit? in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
745

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
768
Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
655

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top