Ive been asked to do a periodic inspection on a couple of properties and when i opened consumer unit covers i found they had both been supplied with what looks like 10mm armoured. I compared cable size to 10mm t ande for the shower and it looked the same size.

I opened the isolator swtich next to the meter and found 100 amp fuse...

ones a bed sit and the other is 2 bed flat.

In the 2 bed flat, they have a hob on 32 amp breaker, mega flo water heater, 25 spots, w machine. 3 x aircon units..

In the bed sit i found 9.5kw shower, ariston water heater, w machine, 14 spots and a stand hob which works off a 13 amp plug top.
 
hmmm

100a fuse protecting a 10mm cable.....

so a 10mm radial can take about 50ish amps (ball park figure, no regs to hand just a guess)
and fuse which can overload by 40% so it may draw upto 140 amps,

Personally I think the cable is a "little" under rated!!!

A code 1 fault and I wonder how it was passed by anyone in the past
 
theres a seperate isolator to each flat
the 2 bed flat run look s under 10 meters and the bed sit is probably about 7meters. Cabling is in partition walls.
No sign of heat damage. Install is quite new.
I only did a visual inspection need to go back and test properly along with load readings
The intake is 100 amp
The aircon units are used for heating aswell
 
theres a seperate isolator to each flat So 1 x 100amp fuse in each isolator. A 70c SWA Erection method C will give you 67 amps so you could downgrade the fuse to 60amp that sorted

the 2 bed flat run look s under 10 meters and the bed sit is probably about 7meters. You will have to downgrade the fuse because both tails are over 3mts and there reg 434.2.1 is contravened

Cabling is in partition walls. Method C
No sign of heat damage. Install is quite new.OK

I only did a visual inspection need to go back and test properly along with load readings
The intake is 100 amp
The aircon units are used for heating aswell

I would recommend you advise down grading the fuse to a 60 in each isolator and code it a 2
 
thanks for pointing that out. I only compared it by looking at the sheathing round the conductor. Didnt check the copper

No probs, i only know because i almost shat my pants after pulling in 50 odd metres of the stuff through a house before checking and then came to make it off and thought **** a rubber duck its only 10mm, but then i realised the sheathing was thinner.
 

Reply to 10 mm supply to flats in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hello everyone, I am currently in the process of estimating the electrical demand for a new construction development that will consist of an...
Replies
0
Views
1K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N
  • Question
Correct flat was paying for e7 just had con unit at basement level. All e7 con units together, only 2 heaters per flat
Replies
13
Views
5K
Good idea James, will all due respect this had to be correct or you have a big mess on your hands and a lot of money spent, trial and error DIY...
Replies
11
Views
3K
  • Question
I have done several similar installations in an SSE area. In two cases I estimated that a 60 Amp supply would be adequate for each flat but SSE...
Replies
22
Views
26K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks