Does anyone have any experience of the SMA 10000TL inverter? I was wondering whether the number of strings had an effect on the 3 phase output of the inverter. For example, does the array need to be arranged as 3 seperate strings?
 
From memory I think the 10000TL has 4 string inputs and the bigger versions have 5. Either way, they are single 3 phase inverters rather than 3 separate single phase units in the same case (if that makes sense) so there is no direct relationship between number of strings and number of phases. You could run it off one string if you wanted and the modules allowed such an arrangement. Currently designing a system using multiple 15000TL's with 2 strings on each.

Something like the Mastervolt XL10 or XL15 is 3 separate inverters in one box, one per phase, so on something like this you'd need at least one string per phase.
 
I'm doing a barn 10kw on a 10000 STPtl at the moment , when we did it on sunny design came out as 2 strings of 21 sharp235's on same input ,
generally if there is an equal no of modules on same aspect ,you'll have 2 equal strings on 1 input otherwise you'll get uneven strings one on each input, as for using all the inputs I don't know how this can be achieved on the design program ,but the new version is coming out soon which will have more flexibility on orientations
Dc combined within the unit giving one output 3 phase.
 
Last edited:

Reply to 10000TL inverter - 3 phase output and number of strings in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
896

Similar threads

Replies
1
Views
515
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top