razz

good morning everyone
in a few weeks time i will have a nice new 1000kva transformer sitting here , i have sent my incoming supply and outgoing supplys to crabtree to have a panel spec`d , but how do i spec the cable from the ct chamber to my panel itself ? i think its gonna be in a metal trunking , any help would be gratefully received

ady
 
If you’re planning on getting 7 X 500mm (cu) or 7 X 600mm (al) in trunking, best of luck, you’ll need it.
You would be better of looking at a pre-assembled busway or ladder rack with aluminium trefoil clamps.
1000KVA is 1333.4A, you ai’nt getting that in trunking easily. I’d be impressed if you did.

Cobrauk, handy PDF but it is for LV incomers. It peters out at 500A this will be 1600A MCCB or fuses.
 
Last edited by a moderator:
Do Crabtree make breakers suitable for 1MVA Distribution Transformers?? I would have personally gone to someone like Schneider to have a panel spec'd, who also have an extensive range of breakers to develop such a panel for you...
 
why seven cables please , thought it would just be the normal 3 ph n + e coming from the ct cubicule as its seems to be called , a busbar system , now you mention it , sounds a good idea , thank you , cobrauk , do you have a 1000 kva document , yours goes to 300 , please
 
why seven cables please , thought it would just be the normal 3 ph n + e coming from the ct cubicule as its seems to be called , a busbar system , now you mention it , sounds a good idea , thank you , cobrauk , do you have a 1000 kva document , yours goes to 300 , please

You'll probably need to parallel the tails off the TX, Even trying to work 600 or 500mm cables is going to be a real work-out for you...lol!!! What tony is calculating is 2 X 500/600mm per phase plus a neutral ...so 7 cables in all!!!
I think you'll probably be better off looking at increasing the number of parallel conductors, to reduce the installation hassle you'll have trying to bend set these large conductors onto connections at both the TX and the Switchboard....
 
ok , thats also a good idea , sounds like its gonna be fun , which ever way i end up doing it , thank you for the replys , i`ll keep in touch on what goes on and how n when

ady :)
 

Reply to 1000kva substation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top