E

ez2own

Hi people would i be correct in saying that the minimum requirements for fixed lighting according to the osg is 10amp for type b breaker for 17th ??? or could you use 6 amp ??

any help most appreciated ....
 
right then....the way to determine this is firstly to add up all the wattages on any loads connected to this circuit then divide this by the nominal voltage...so for instance you can go...1100W/230V=4.78..which is the amps. So in this case a 6A MCB would be ok. It all depends on how many loads are connected and the rating of course.....
Hope this helps.
Glenn.
 
Cables have to be able to carry the current demand and as hifly....comply with disconnection times etc. one of The rare ocasions where you might want to choose a c type MCB is where you have inductives whic have high inrush currents...such as moters and non-incandescent lamps etc....
 
right then....the way to determine this is firstly to add up all the wattages on any loads connected to this circuit then divide this by the nominal voltage...so for instance you can go...1100W/230V=4.78..which is the amps. So in this case a 6A MCB would be ok. It all depends on how many loads are connected and the rating of course.....
Hope this helps.
Glenn.

cool glennspark , thanks all wattages are bang on so 6 amp more than enough .
 
what if they using floursescent fittings , would you still use this quick method glen;)
right then....the way to determine this is firstly to add up all the wattages on any loads connected to this circuit then divide this by the nominal voltage...so for instance you can go...1100W/230V=4.78..which is the amps. So in this case a 6A MCB would be ok. It all depends on how many loads are connected and the rating of course.....
Hope this helps.
Glenn.
 
as long as your either on or under the rating of the MCB then yes. The thing to remember though ez....is when you start going onto c and d type MCBs ....your Zs is a lot tighter with these types of overcurrent devices so it would be prudent to only use them where absolutely required otherwise your cutting down your chances of compying with disconnection times.........
 

Reply to 10a or 6a (lighting ) in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

By code the washing machine needs its own 20 amp single pole GFCI circuit, the dryer needs a 30 amp double pole breaker and using # 10 wire. Your...
Replies
1
Views
789
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top