I know the difference between the 2 sorts but I'm thinking do I need to fit 10KA breakers in this scenario, when I've got 6KA MCBs in the van!
3 phase DB, Isc 4.9KA (phase to earth), all circuits from this DB are single phase. Will never be 3 phase in future (HMO).
Worst case short circuit (phase to phase) would be 9.8KA, but that could only happen in the DB itself, which is protected by the 100A 1361 DNO fuse.
3 phase DB, Isc 4.9KA (phase to earth), all circuits from this DB are single phase. Will never be 3 phase in future (HMO).
Worst case short circuit (phase to phase) would be 9.8KA, but that could only happen in the DB itself, which is protected by the 100A 1361 DNO fuse.