quickspark

Hi Folks,
we building 6 storey block of flats and need a quite few 30 units of 10kva transformers connecting up to the mains. At the moment we have five trafo on 32A type C braker and that gives us a proper headache with its nusianse tripping, even without any load. Can anybody tell us how many maximum trafo we can have on one 32A breaker?
Many Thanks in advance.
 
having 10kva transformers on a 32a type c breaker will invariably cause nuisance tripping, as a guide type c mcb's allow for inrush on motors or small transformers but a type d would be better for the inrush of a large 110 transformer, if more than one is plugged into the ring then i suggest switching the transformers on one at a time as the combined inrush of more than one trnsformer would be a feat for even a type d breaker.
Once you've switched each transformer on seperately the no' allowed on a 32a breaker is all dependent on the load they demand as unloaded they use little current while energised.
 
I seem to remember from my college days that the the transformer VA rating is divided by the secondry windings, as a rule of thumb but there is a mathmatical way of working it out but i cant rember it.
so 10,000/240=41.6 amps
 

Reply to 10kva three phase site transformers in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
There CT stands for current transformer. Basically for meters up to around 100A they are usually directly connected, i.e. the current passes...
Replies
10
Views
3K
  • Question
Most 30mA RCDs - in reality - trip around 22mA. So no, it would be risky! You may have to consider alternative means of protection (e.g...
    • Like
Replies
11
Views
4K
  • Question
Thanks for that advice. I don't know the MV capacity locally, though there are lots of wind farms several miles away so generation is not such a...
Replies
2
Views
900
  • Question
Ok Dave thanks, no more accidents yet 🙏😂….
    • Like
    • Informative
    • Winner
Replies
6
Views
2K
  • Question
Probably not, water is not my problem :) 2/3rd and 1/3rd is the last option but not fully satisfactory. That is why I have been trying to find...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks