Thanks Dave I was editing putting in the bit about convenience.
The T&E is buried. in the wall. I'll wire tommorrow and report back.

For testing during the install I will do continuity and IR from the cu to the junction box .
Then test from the armour to all the cores - then IR Would that be sufficient.
 
Thanks Dave I was editing putting in the bit about convenience.
The T&E is buried. in the wall. I'll wire tommorrow and report back.

For testing during the install I will do continuity and IR from the cu to the junction box .
Then test from the armour to all the cores - then IR Would that be sufficient.

You need to test the complete circuit to get your R1+R2, although it could be done in two stages there is no need to do so in your case.
Same goes with IR.
The issue with doing the tests in stages is that if you then make connections after doing the tests then those connections have not been tested.
 
if the house is pme and you have extraneous metal in the shed, then that cpc in the 10mm T/E will be undersized. you'll need to paralle some 10mm Gn/Y with it.
 
The cable's mine now. I would offer him a nice drink, but he's gave me the cable in lieu of a favour i did him. :teeth_smile:
Been doing some cable calcs, hmmm I could have a tumble dryer and a chest freezer down the shed, then the missus would owe me a favour :tt1:


Lucky your not married to my missus.............hey darling I moved the tumble dryer and the chest freezer down to the shed for you ............

The second word from her would be off................
 
Lucky your not married to my missus.............hey darling I moved the tumble dryer and the chest freezer down to the shed for you ............

The second word from her would be off................
We haven't got a tumble drier or a chest freezer - no space in kitchen for them.:hurray:
 
if the house is pme and you have extraneous metal in the shed, then that cpc in the 10mm T/E will be undersized. you'll need to paralle some 10mm Gn/Y with it.
TNS supply

Please can you put me out of my misery and say if that's OK ?:D
 
Last edited by a moderator:

Reply to 10mm 4 core SWA in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
352
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
901
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top