I have a 10mm 4 core glanded into a length of conduit buried in the wall, around 2 metres in length, I tested continuity between all cores and galv conduit and it's perfectly clear, however when I tested IR it failed between 2 cores and conduit. Am I missing something here or does it simply need replacing? Cheers


---
I am here: http://maps.google.com/maps?ll=54.089885,-0.199081
I am not a number! I am a free man!
 
is either core earthed? are you getting a false reading from a neutral to earth due to parallel paths?
 
possibly not picking up fault on continuity due to low test voltage,if your doing IR test them you have 500 volts going through,try doing your continuity using the same setting as your IR test it,s suprising what doesn,t show on a continuity that an IR picks up.thats why we do IR test at twice the working voltage. hope this clears things up
 
I have a 10mm 4 core glanded into a length of conduit buried in the wall, around 2 metres in length, I tested continuity between all cores and galv conduit and it's perfectly clear, however when I tested IR it failed between 2 cores and conduit. Am I missing something here or does it simply need replacing? Cheers --- I am here: Google Maps I am not a number! I am a free man!
If the IR is low or you get a dead short, check if they haven't driven a nail through. ... or any bare leads touching the galvanised conduit.
 
Last edited:
Cheers guys the cable ain't terminated either side, I ran it in myself, I dont know what prompted me to test it in the first place but kinda glad I did, I guess I'm gonna have to replace it though since the insulation ain't upto scratch, just can't see why it would fail IR unless it's a manufacturing issue?


---
I am here: http://maps.google.com/maps?ll=54.089741,-0.199005
I am not a number! I am a free man!
 

Reply to 10mm armoured need replacing? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
832
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
930

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top