I have a job where the client wants a 7kw car charger 50 meters away from his house. The problem is there is a 6mm that's been pre wired 10 meters through his house from the main consumer unit to an exterior wall and sealed up. So I would have to use that and join onto the 10mm exterior and put on a 32amp MCB. Can see any issues doing this?
 
Why 10mm ? Depends on cable run and voltage drop.
Assuming the 6mm is TandE then barring anything too exotic you will be good for a 32/40 amp mcb.
I had a few instances of a ev charger tripping a 32 amp mcb and some manufacturers recommend a 40 amp.
Might be worth checking?
You could look at taking 2 core swa from the existing cable in suitable outdoor box. Keeps costs down, Using armour as cpc in cable run. Dont terminate the armour as the earth at charger as you will use a rod.
It is late and without doing the calculations on voltage drop you might manage to use 4mm 2 core swa depending on install method but 6mm 2 core swa will almost certainly be adequate . Saves using 10mm.
 
Hi - can I ask what is it you are concerned about? Is it the voltage drop, the ccc change, the cpc size and the earthing system of the installation, the cable installation method and jointing, or ... :)
 
Hi - can I ask what is it you are concerned about? Is it the voltage drop, the ccc change, the cpc size and the earthing system of the installation, the cable installation method and jointing, or ... :)


Voltage drop mate. Just seems illogical way round. I'm running 2 core 10mm to charger exterior and making a tt island at source.
 

Reply to 10mm joined to 6mm for exterior charger in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
710
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top