Come across this twice now - what's everyone doing with this I'm advising my customer it should be a bigger cable but it the old well it seems to work ok
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 10mm T&E 9.5kw shower loads of new insulation in the Australia area at ElectriciansForums.net
IMO if your running T + E the only way you will get compliance with the regs is Method C clipped direct, as that will give you 47 amps for 6mm^
Even at 240v which most showers are rated at it will still be 39.5amps so I would fit a 10mm