10mm Tails size | on ElectriciansForums
Discuss 10mm Tails size in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
newfutile
Nearly Esteemed
Supporter
hemel hempstead
During a recent EICR I have found 10 mm supply to the flat
This is fed from a Locked ryefield DB though a meter then a double pole 100 amp
Isolator , the outlet from the isolator is the 10mm 3 core possibly hightuff cable
This is over sleeved into the isolator.
My question is would the suppliers fuse if appropriately sized protect these cables?
And how to ascertain the suppliers fuse size or should this have a separate fused Isolator ?
Short answer is that you'll never know without inspecting the fuse in the carrier. Longer answer - how sure are you that they're only 10mm? Easy to confuse for 16mm. 10mm 6181y is rated to 65A so could well be a 60/63A service fuse in the Ryefield - I'm assuming this is part of a BNO system?
I’m not 100% sure as they have no markings on them and I have just sized from eye , it is probably part of a BNO system as the ryfield feeds many meters and isolators to a group of flats
If they look like High Tuff which would be unusual for that type of circuit they could alternatively be split concentric.
You can compare the size to the 25mm tails here , even so I would need to confirm the fuse size and whether it’s permitted for this fuse to protect those cables
Ermmm...... what size trunking is that? Those don't look big enough to be 25mm tails.
Reply to 10mm Tails size in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...