calv68

Hi everyone ive been to look at a board change in a two bedroom flat the db is supplied from a meter room with 10mm twin & earth via a 63 amp switch its a tncs system. The earth from the met in the meter room to the 63a isolator is 16mm but from there to the db is only 4mm coming from the 10mm twin & earth, its clipped direct so can draw 64 amps is this within the regs
 
Just answered a similar question (25mm t&e if you have a look), if an earth wire supplies the earth path for multiple circuits then its required to be equal to or greater than the associated phase conductor also take into account if equipotential bonding is required from the submains then an allowence in csa of earth must be considered too.
 
any chance of explaining the point on equipotential bonding from a submain , in regards to csa.
great aswer, well explained, many thanks darkwood.
Its just a reminder that the incomming supply denotes the size of the equip' bonding conductors especially where tncs(pme) systems come in, and your equipotential bonding may exceed the submain earthing size even with your additional earth thus requiring a larger earth to each flat as they may need to be treated as a seperate installations with regards to equip' bonding depending on the building layout thus requiring local equipotentail bonding to submains.
 
Last edited by a moderator:
Just answered a similar question (25mm t&e if you have a look), if an earth wire supplies the earth path for multiple circuits then its required to be equal to or greater than the associated phase conductor also take into account if equipotential bonding is required from the submains then an allowence in csa of earth must be considered too.

Can you clarify where it says this in the regs please
 
Can you clarify where it says this in the regs please
Check out reg' 543.1.2 and when talking about the equip'bonding and allowing for it, if you have a common supply to multiple premises and each unit is independant with its own access it must be regarded as a seperate installation and thus bonded at the imcomming point to said premise, this regulation spans further than the red book but into fire regs and building regs, so if the main bonding requires 25mm at origin it will also require the same at common premises to supply:- therefore the earth to said premises needs to be adequate to allow for equip' bonding. This is more so when dealing with TNCS as eddie curents can circulate around the earthing system hence the larger cables required compared to TNS.
I fell foul of this myself as the regs dont mention this situe but the NICEIC inspector got me on it, but after the explanation i can see the reasoning behind it.
 
Last edited by a moderator:
Check out your on-site guide, P15 & 16, "General layout of equipment"

if you have equipotential bonding going to the C.U. fed from the 10mm t&e then your earth is not big enough. I would run a 16mm myself :)
 

Reply to 10mm twin & earth supllying DB in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top