Question 1

Is a flood light omitted from over current protection?
I normally go a lighting circuit but this job would be a lot easier if coming from the outside socket, which is part of the ring,
As this is fixed, would it be okay to wire it in 1mm or 1.5mm flex, without over current protection, eg like a spur I guess as this doesn't.

Question 2

Would you be happy feeding a 10w led flood light from a sour socket, as its such a small load?

I would say yes to both but I've had people say no you can't .
 
Isolation requirements for adjustment, general maintenance etc
Reduction in cable size on the ring would require appropriate down fusing over 3m ( Supplying fixed load )
Zs would still need to comply (You have reduced the earth size thus increased the Zs Value against the 32amp mcb/rcbo)

Yes in theory you could wire direct to a 32amp mcb in the board with 1mm cable but as you are asking about tapping onto a ring then you have other regulations to consider here, with the exception of socket circuits, most house circuits can be classed as fixed loads if you know the max' demand possible, we of course don't do this in practice in domestic as its not the done thing and can be very confusing to others who follow so we all tend to design and wire without using the omittance clause.

If the light was within a 3m run of a socket it was tapped off then yes you could argue it is within regulation to do this but just from a maintenance aspect, I would be running it through a suitable Sw/F spur. Also to note, the manufacturers instructions may require fusing down but this is manufacturer dependent.

In my sector this clause comes into its own as I use it regular when allowing larger breakers to counter nuisance tripping due to inrush on fixed load equipment.. this be more the targeted application of this regulation.

Personally in my opinion, you shouldn't be looking to use this clause in domestic like in your example, add a fused spur as is the general practiced method.
 
Last edited by a moderator:
The spur via a FCU, your max Zs would change as it would be protected by the 1362 fuse in the FCU so the max Zs for the light via a 3A fuse is something like 17ohms

no it wouldn't as you would spurring of the Ring final circuit to add the FCU in so the OCPD recorded on the minor works would be the one in the board.
 
Customer wants least mess possible, and isn't doing it in 2.5 the same as an infused spur Anyways??
In the osg it states an unfused spur can be one single or double socket or one perminately connected appliance ?

What's messy about a suitably IP rated FCU close coupled to the outdoor socket ? Has it been confirmed that the outdoor socket is within the RFC properly as it is common practice to spur off for an outdoor socket addition ?
 

Reply to 10w led floodlight /protection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Replies
5
Views
1K
Problems can arise when you get on too well then they think he won’t mind me doing a bit.
    • Friendly
    • Like
Replies
8
Views
472

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top