hi folks am i missing something here on a tt system ze is 19.9ohms and supply obv 230v giving a pfc of 11.5ka so if the mcb type b is rated at 6ka is this a problem? apologies in advance if im bein thick:D
 
hi folks am i missing something here on a tt system ze is 19.9ohms and supply obv 230v giving a pfc of 11.5ka so if the mcb type b is rated at 6ka is this a problem? apologies in advance if im bein thick:D


11.5 amps more like??

0.012ka

If i've done the maths right.... It is off the top of my head so I'll hold my hands up if wrong!

Jim
 
Last edited by a moderator:
If its a tt system that then dont worry to much about the low fault current as RcDS will get it. (maz as for 30ma rcd 1667ohms) Be carefull with your maths wright calculation wrong symbol at en. it can cause a lot of problems and will get failed in exams.
 
I'd agree with Jim, I wouldn't expect a fault current anywhere near that high on a TT system.

Been testing on TT's all week funnily enough all around 45 - 50ohms Ra and fault currents of 20 - 30A, 0.020 - 0.030KA.

As a side note manufaturers will guarantee their MCB's (6KA ones) installed in consumer units to BS.........(the number fails me at the mo) to a maximum of 16KA.



Edit.....BS 60439-3.
 
Last edited by a moderator:

Reply to 11.5ka? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
506
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
Replies
8
Views
768
  • Question
I answered a similar question for the client, just looked at all the heaters (2KW per heater) and then asked for their half hour consumption...
Replies
7
Views
850

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top