110 V between L and CPC | on ElectriciansForums

Discuss 110 V between L and CPC in the UK Electrical Forum area at ElectriciansForums.net

Joined
Oct 30, 2017
Messages
113
Reaction score
59
Location
Scotland
I am in training and decided to do some dead tests using my second hand Fluke MFT 1653B on an upstairs ring. I did the tests at a socket rather than at the CU. Results end to end L - L 0.74 ohms, end to end N-N 0.76 ohms, end to end cpc >2000 ohms. I checked all the sockets on the ring and couldn't find a break in the cpc. With the circuit energised I'm getting 110 V between L and cpc at the test socket as well. No idea what's going on. The cu is fully RCBO. Any help would be appreciated.
 
Sounds like the cpc is broken in two places, and you are picking up capacitive/leakage voltage on the floating portion.

Carrying out dead tests, link one end of the cpc with the corresponding L then do a continuity test at each socket outlet by just plugging in the mft checking L-cpc. As you work around you will find the last one with cpc, and the next without (so a break between them), then repeat for the other leg of the ring. You should be able to find the cpc breaks quite easily.
 
Re your 110V reading on the energised circuit, if there is anything plugged in (or even something forming part of the fixed installation) that has an interference filter in it (which typically includes capacitors from L and N to E), then that can give half line voltage on a disconnected earth when measured with a hight impedance tester. It implies that part of the CPC is open circuit.
 
As above, a floating section of CPC will tend to take up a voltage somewhere between line and neutral/earth potentials. The more symmetrical the leakage pathways, the nearer it approximates to a 2:1 voltage divider and if cable inter-core capacitance is the main factor, the longer the cable run the lower the source impedace of the 'ghost' voltage. With T+E, where the capacitance from to each live core is very similar and the stray capacitance to the otside world is minimised by the layout of the conudctors, a long run can produce quite a convincing 50% of line volts, usually pulled down a bit by the input resistance of the meter and the stray to real earth.
 
Thank you all for replying, I appreciate that. I followed Julie's advice and linked the cpc and L from each leg and did get continuity from different sockets depending on legs. There are 8 sockets on the ring (and 1 spur). From one leg I got 6 giving continuity and 2 with >2000 ohms. Swapping the legs I got exactly the opposite (2 working and 6 not). Unfortunately I have no idea how the cable runs between each socket. Is all I'm left with is lifting boards and going in the loft? Also, I got perfectly acceptable Zs figures for each socket - don't understand that. Anyway, thanks again - every day is a school day.
 
You can do a similar test to find the wiring route or at least get some idea, take both ends out, Link L and CPC again on one leg and measure the resistances, the resistance will increase the longer the wire is and therefore this gives a good idea as to the order the sockets are wired.
If there are no spurs, the break should be between the sockets with the highest resistance reading when you link each end in turn. The other leg needs to not be joined for this to work.
Hope that makes sense, it's easier to do than describe!
 
Thank you all for replying, I appreciate that. I followed Julie's advice and linked the cpc and L from each leg and did get continuity from different sockets depending on legs. There are 8 sockets on the ring (and 1 spur). From one leg I got 6 giving continuity and 2 with >2000 ohms. Swapping the legs I got exactly the opposite (2 working and 6 not). Unfortunately I have no idea how the cable runs between each socket. Is all I'm left with is lifting boards and going in the loft? Also, I got perfectly acceptable Zs figures for each socket - don't understand that. Anyway, thanks again - every day is a school day.
Well it sounds like you know where the break is, i.e. between which two socket outlets, now is the difficult part - finding the cable route, if there is a spur, then it may be there is a jb in this portion of the run, finding it is a matter of working out the path - how the cable leaves the socket, - which is the logical path to the next socket etc.

This needs to be addressed, you can't leave the ring as is, either sort it, or change it to two radials (max 20A RCBO not 32A), and remove any socket with no proper cpc connection.
 
You can't just leave the faulty cable connected. Both ends of it must be completely disconnected from their respective sockets.
If the bank of MCBs is protected by a RCD, and the max amps rating of that RCD is lest than the upstream fuse protecting it, then the sum of your individual MCB ratings, added together, including the extra 12A you are introducing, must be less or equal to the RCD's rating.
 

Reply to 110 V between L and CPC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
273
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
267
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
296
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top