The plumber at my company went ahead and fitted a 12kw electric boiler without first checking the main supply to the flat. Now I'm guessing if its only a 60a main fuse with 4 ring circuits and 1 lighting circuit, the probability is that it will blow the main fuse at 60a. I couldn't locate or get access to the supply yesterday.
Ohms law says that the boiler is capable of drawing 52a. I was thinking of putting it on a 50a circuit with a short 10mm twin and earth run of about 1 meter.
The old style mk fuseboard does have a 30ma main rcd switch, so the circuit would have rcd protection.
My other dilemma is can i still get the old style 50a mk ln5932 fuse???? Someone told me the new mks should fit ok.
I'm guessing that they may have to change to a 9kw boiler if the supply isn't 100amps???
Cheers
Ohms law says that the boiler is capable of drawing 52a. I was thinking of putting it on a 50a circuit with a short 10mm twin and earth run of about 1 meter.
The old style mk fuseboard does have a 30ma main rcd switch, so the circuit would have rcd protection.
My other dilemma is can i still get the old style 50a mk ln5932 fuse???? Someone told me the new mks should fit ok.
I'm guessing that they may have to change to a 9kw boiler if the supply isn't 100amps???