Taylor_J

Hello all!

I've come across a bit of a problem today as I was changing a socket and got a tingle (Isolated the MCB of course).

I tested the voltage and it was pulling 12v.

I've found when you isolate the upstairs lights the 12v on the upstairs sockets disappears.

Its a 17th edition dual RCD split load board.

The upstairs socket ring is on the first RCD and the upstairs lighting circuit is on the second RCD.

Any one got any answers for this problem or has anyone come across this before?

Thank you :)
 
think it's a question of dissing each circuit from CU and testing between circuits to see if there's some sort of inter connection, possibly coupled with a poor connection on one of the circuits.
 
That probably isn't very helpful to you! My guess would be induced voltage. I wouldn't have thought there'd be any real energy behind it. Do you understand about induced voltage? Not trying to show you up, but it can seem a bit unbelievable.
 
That probably isn't very helpful to you! My guess would be induced voltage. I wouldn't have thought there'd be any real energy behind it. Do you understand about induced voltage? Not trying to show you up, but it can seem a bit unbelievable.

Haha no worries. Electromagnetic I take it? To be fair mate I have never come across this before in 10 years of house bashing. It just threw me a bit. The loop impedance, insulation resistance, rcd and r1+r2s all came out fine.
 
Could be just induced voltage....although you wouldnt expect a tingle from that. Only answer is a testing session at the DB
You can receive more than a tingle,from an induced voltage,depending on the circuits doing the inducing,and the ones being induced. Any equipment connected to other circuits,MAY have the capability to "hold" some of that inducement.
If you imagine how a transformer functions,with both sides separated via insulation,it is not hard to imagine the generating of substantial voltage,as conductors wind their way around each other,especially when bunched.
Try it out,with two lengths of T&E,and a horse-shoe :icon12:
 

Reply to 12v on socket ring main after isolation. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top