Well the oven turned up today. Despite the Bosch site simply saying "13A" on the back of the actual oven it's written 2.35KW". Thought the site would have been more specific than 13A and also that the 2.35KW would have been written properly 2.35kW - so much for Germanic engineering proficiency etc! Me being picky I know but you have to have standards!
The Bosch online "Technical Specs" says "Current 13A". So 2.35kW at 230V and we get (only) 10.2A. Even with voltage tolerances (230V +10%, -6%?) I can only get as high as 10.8A.
Its suggestive to me that by this "13A" that its ok to plug straight in to a socket BUT reading the instructions and they say "Mains connection lead HO5 W-F or higher" then "An all pole isolating switch with a contact gap measuring at least 3mm must be available during installation".
No problems on the cable but the switch and this "all pole" business? Obviously the 20A DP switches are double pole but are the cooker type switches "all pole"?
Best option I assume would be a dedicated radial (thus complying with the "over 2kW" reg) with a 16A breaker in the board - not a current option until I change the board followed by a cooker switch above the worktop. Then an unswitched socket and 13A plug top below the worktop. Was thinking cooker connection plate or flex outlet here instead of the plug top............?
With the lack of spare way in the CU I'm thinking DP switch off the ring to an unswitched single socket outlet then plug top with a 13A fuse in.
Anyone see that as a problem?
Cheers