Hi. I found a radial power circuit on an EICR yesterday wired in 6mm2 flat twin PVC cable and have some concerns. I know that the MCB is designed to protect the cable but what about the terminals of the sockets? 13A socket-outlets are rated to 20A max and I am not sure they are designed to have 2 x 6mm2 conductors in the terminals? I thought they were designed for 3 x 2.5mm2?
Someone could plug lots of appliances into the last socket on the circuit and overload the terminals, but the MCB would not disconnect. Should I code this?
Thanks
 
The 20A limit (I think) you mention is for the load on a double socket, not the through-current on the terminals.

The basic principle behind 13A plugs and sockets is they have the protective fuse, so it does not matter (within reason) what the supply is, so long as the supply cable is protected. After all cooker switch/outlets often have up to 45A MCB feeds.
 
Someone could plug lots of appliances into the last socket on the circuit and overload the terminals, but the MCB would not disconnect. Should I code this?
Thanks
Would be limited by 13A fuse in plug, or 26 between two, as any other wiring method.

Not worth a code, but maybe a note.
 

Reply to 13A BS1363 socket-outlets on a 40A MCB in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My wife’s Evoque gets about 32 miles on a full charge and I get about 28 miles on my F-Pace. I don’t know how long a full charge takes but I...
Replies
13
Views
1K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
787

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top