13amp oven to connect | on ElectriciansForums
Discuss 13amp oven to connect in the Talk Electrician area at ElectriciansForums.net
salisbury spark
Best way sought to add a oven (13amp plug top) to kitchen
Loads of ways - some safer than others!
Sould i add a FSU13amp spur off ring main(taking into consideration existing loading).
OR
Some arrangement from the back of existing cooker switch to hob(bearing in mind need to protect the new oven circuit with lower 'fusing').
thanks
6mm link from cooker outlet to single socket at side of cooker outlet,plug top fuse (on oven flex) will give you your protection.Cooker switch will also provide isolation point (obviously the cooker supply cable will be 6mm also,if you were to use a 6mm link ).If the cooker circuit is in 10mm then you will struggle to get everything into a cooker outlet :confused:
Cheers SCHOL1.- Didnt consider a socket from the cooker outlet (didnt think 6mm would go into socket) - thinking about it it should.
Answer provides everything i was looking for thanks.
Reply to 13amp oven to connect in the Talk Electrician area at ElectriciansForums.net
First thing to say is that it's desirable to have a method of isolation for the oven somewhere near it in the kitchen, and not hidden behind a...
allowing for diversity a 32 amp supply will be fine for them both, but remember, the cable needs to be adequate to cope with a load on up to that...