Been asked to run a feed for a 15kva transformer over about 40 meters for a site transformer. SWA Cable will be underground any suggestions on sizes and protection? Also would it be best to drop the transformer out and put a board in instead (as I have a spare three phase board hanging around my yard somwhere?
 
ive just done some v basic calcs. im guessing at a PF of 0.8, and arrive at at a figure of 45A from your tranny. I would install a 16mm SWA, and run it in ducting, to facilitate replacement, and to provide a new cable route. I would use a bs88 fuse, as it will comply with Zs, where if you use a MCB D type to 40A, it will not, and you will have to up your cable size to 25mm2

THE ABOVE IS WRONG, I messed up the calcs!
 
Last edited:
Bear in mind that the above was based on a TNC-S system , with a Ze of 0.35. in reality, your Ze will probably be lower, and you may get away with a D type MCB,. but please check first.
 
... it's a TNCS system Ze = 0.11 ohms - 40 meter run - it's on a bulding site and will be used to power 110v accsessories until the build is finished. I was wondering if i can take it straight out of the head into a rotary isolator with outlet to the transformer? If so what protection and where? Would 10mm be okay?
 
On 10KVA 3 phase transformers I use 4mm 4Core SWA on a 32A type D.

The fourth core is soley for added earthing security as more often than not transformers take a bit of punishment on site and glands are regularly pulled out.

Bear in mind this must also have RCD protection.

Hope this helps
 
As you say the cable is to feed the transformer the FLC will be 20.8A @ 415V so work from there. As has been pointed out expect damage to occur so protect accordingly.
I installed a temporary transformer in a steel stock ground a while back it was reduced to scrap within two days despite having a girder frame around it
 
I would also be mindful that you can allow a fair amount of diversity even though it is a single point circuit. I have carried out regular load testing on a variety of 10Kva transformer circuits ( up to 3 on radial ) and the highest loading i have seen is around the 10-12A per phase mark.

As I said before, this MUST have rcd protection if on a building site.
 

Reply to 15kva Transformer in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
184
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
560
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N
  • Question
Thanks for the input guys. Lighting track is out of the question. The routing (h section guirders and angle iron) means that swa cable clipped...
Replies
12
Views
2K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top