MHK

Howdy

I've come accross a situation where 16A MCB have been specified for ring circuits. The rings serve socket outlets having looked through the regulations I have been unable to locate any specific requirement stating that they can not be used, however, I would be grateful for some alternative views!

Many thanks in advance :)
 
The query wasn't necessarily as to whether you can or can't use 16A rings. There are approximately 200 ring circuits specified on 4.0 XLPE/LSF singles protected by 16A MCB breakers. I could understand if the intention was to reduce cable sizes by reducing the breaking capacity, however, this is not the case. I can really understand the benefit of wiring in this way?
 
Nothing wrong with using 16A ocpd for a ring final & you'll not find anything in the regs that says otherwise.
How big/long are the rings & what is the customer use.
 
The most likely reasons for the specification of 4mm[SUP]2[/SUP] XLPE (90 degree C operating temperature) and 16A MCB is this cable and it's protective device has been downrated because the cable is run through significant amounts of thermal insulation and/or areas of high ambient temperature and/or large number of cables grouped together.
 

Reply to 16A MCB for a Ring Main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
663
  • Question
Thank you for the speedy response! Have seen them on top of plaster in steel conduit before but guess it's not a common desire to have wires...
Replies
2
Views
701

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top