16amp radial | on ElectriciansForums

Discuss 16amp radial in the Australia area at ElectriciansForums.net

D

Doble89

I have installed two rcd sockets in a plant room where I work I done this using 2.5 swa cable on a 16amp rcbo as there sockets will rearly be used the length is 15 m long is this ok
 
I disagree,
if there is a neutral to earth fault which device would trip?
unless there is a time lagging device like you have in a site MDU,
either the RCD or RCBO could trip and could result in a headache later
I would suggest that you downgrade the RCBO to an MCB.
The SWA has earthed armouring so an RCBO is not require

Richard
 
Last edited:
I think the OP means the sockets are RCD protected by having used an RCBO. In which case all is well.
 
yes I understand that,
if there is a Neutral to Earth fault on the device that is plugged into the RCD socket then there are 2 Residual Current devices in series in the circuit.
As I stated before either of the RCD, or the RCBO could trip.

If my reading of the OP is correct then they aren't 'RCD sockets' - just normal sockets connected to an RCBO.
 
I have read it about four times,it says to me,t he has run one swa 2.5mm fed from 1No 16amp rcbo, terminated to feed 2 No rcd sockets

Its a good enough confusing statement to compare with a lot of the regs
[ElectriciansForums.net] 16amp radial
 
Doble - could you please enlighten us?!
 
Well Rockingit, at least we agree about somthing

I also don't disagree with you that if he HAS installed RCD sockets on an RCBO circuit then it's not a good solution!
 
I thought it was just me that had been on the pop.......
 
Must admit, it reads to me that the socket-outlets are RCD type, and they are also protected by an RCBO.
Don't see the need for any RCD protection, unless the socket-outlets are to be used for mobile equipment outdoors?
 

Reply to 16amp radial in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
940

Similar threads

  • Question
Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many...
2
Replies
25
Views
2K
nicebutdim
N
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
154

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top