Evening all,
I have a question regarding calculation of CPC on a 16mm T+E and wondered if you could help at all.

I have done a board change and the supply is via a 16mm T+E. It appears the CPC is 6mm and therefore I did the adiabatic equation to confirm if the CPC is adequate.
The circuit is fed via 60A BS1361 type 2. The issue I have had is that BS1361 is no longer listed in appendix 3. Does any one know what table in appendix 3 should be used? Looking through the green book it appears that the equivalent would be BS88-3?

I therefore did the following calc. S = √ISq t/k
TN-S system
My Ze was 0.12ohms so fault current is 230/0.12=1916A
K value was 115 as cables bunched with other circuits (taken from table 54.3)
1916A squared = √3671056 x 0.1S disconnection time. (i assume due to the fault current and reference to table 3A1 it would be 0.1S) = 605.892/115 = 5.26mm CPC

Therefore 6mm would suffice.

If anyone can confirm or correct this I would be grateful. I still find the idea of using anything so small as uncomfortable, but if it complies then I am happy.

Many Thanks
 
you dont use Ze for the fault current calc in a adiabatic check , you use Zs , or in this case the Z at the DB.
and yes bs 88 is the "new" 1361
 
You need to obtain a copy of the pre-amendment Regulations, or look up on google for the time/current characteristics.
BS88-3 has replaced BS1361, but the time/current characteristics are different.
 
You need to obtain a copy of the pre-amendment Regulations, or look up on google for the time/current characteristics.
BS88-3 has replaced BS1361, but the time/current characteristics are different.
Spot on with that. It is essential you locate the time / current characteristics for the fuse installed as this may well be the difference between a satisfactory outcome or a non compliant supply requiring upgrading which another spark will gladly shoot you down on if he prooves your calculations were incorrect.
 

Reply to 16mm T+E and adiabatic equation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
262
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top