C
craig1000
Existing supply is 16mm T & CPC to 2nd floor floor flat from ground floor communal CU! Fed via BS1361 60amp, after the incoming mains have been split between 2 meters! Incoming main fuse only 60amp too!
Loop reading @ 2nd floor CU is 0.12 & PFC is 1.87kA respectively!
Bit of an existing mess to be honest IMO, there are 2 6mm single cpcs running up from the MET, both go to the flat CU, there is then from the flat CU another 6mm cpc going to water under kitchen floor!
No gas bond at present in the flat itself but gas is bonded in ground floor lobby from MET.
Main water supply is also bonded in attic above communal lobby & then splits itself to go up into 1st & 2nd floor flat!
My view is I can leave how it is as the water is bonded as a whole into the building, does it then need bonding again entering each flat? If not then gas is already bonded on entry to the building, both flats have separate metered supply & separate bonds from MET to each gas meter!
This being the case then the 16mm T & E suffices as a supply cable only does it not? Or if needed could the 2 * 6mm single cpc's be utilized? Pig of a run to alter anything & would like to avoid if poss for cost reasons for customer! If it has to be done then so be it & customer understands!
Loop reading @ 2nd floor CU is 0.12 & PFC is 1.87kA respectively!
Bit of an existing mess to be honest IMO, there are 2 6mm single cpcs running up from the MET, both go to the flat CU, there is then from the flat CU another 6mm cpc going to water under kitchen floor!
No gas bond at present in the flat itself but gas is bonded in ground floor lobby from MET.
Main water supply is also bonded in attic above communal lobby & then splits itself to go up into 1st & 2nd floor flat!
My view is I can leave how it is as the water is bonded as a whole into the building, does it then need bonding again entering each flat? If not then gas is already bonded on entry to the building, both flats have separate metered supply & separate bonds from MET to each gas meter!
This being the case then the 16mm T & E suffices as a supply cable only does it not? Or if needed could the 2 * 6mm single cpc's be utilized? Pig of a run to alter anything & would like to avoid if poss for cost reasons for customer! If it has to be done then so be it & customer understands!