I've done a periodic on a small office today in the cellar there is a switch fuse with a 16mm T+E feeding a DB on 2nd floor with 2 ccts for offices with computers and a lighting circuit. The office ccts will have high earth leakage from computers 10+ on each circuit. The DB should therefore have dual earth as rings for the computer ctts an be classed as code 4.

Any helps please guys
 
I could stand corrected here but I did not think that applied to distribution circuits...just finals...after all how far do you go? dual earths from the earth source to the MET?
 
Do you mean dual earth of the distribution circuit?
I'm not aware of any requirements for this and I would imagine that a distribution circuit cpc would be regarded as mechanically robust enough not to need duplication etc.

Remember that high integrity earthing is purely to increase mechanical integrity of the connection(s).
 
Last edited:
I think he means the computers circuit
If the leakage exceeds 10m/amp they require high integrity connection
If they are on a ring however and that ring is 2.5mm/1.5mm then the total area is 6 cores which together is 12mm it exceeds the size required (10mm total of all cores of a multi core cable,It just needs connecting as high integrity at the consumer

Oh sorry
I just re read the topic title,theres me waffling on about something I know little of and the title says 16m T+E for dusl earth :eek:
 
Last edited:
And at the sockets...

Why mention the 16mm?
 
Last edited:

Reply to 16mm T+E need for Dual earth? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top