Hello everyone,
I have recently qualified, though yet to start practising, as an electrician.
I have noticed, at my home, the tails from the (single phase) 100A mains cut out to the 100A rated meter, from the meter, to a 60A isolator and from the isolator to the antiquated fusebox are all 16mm. I have looked up on this forum and elsewhere about 16mm tails on 100A supplies, so I am fairly up to speed on the debate, but ...
This is my thinking: BS 7671 110.2 (i) excludes systems for the distribution of electricity to the public from 7671, but would not BS 7671 regulations still apply when reconnecting meter tails as these would be part of the domestic installation even if the cut out fuse was regarded as part of the distribution system? (NB at this point I am not saying necessarily that the 16mm tails would be a violation of BS7671, it’s more an academic question as to whether the person/organisation replacing the cut out is subject to IEE regulations when reconnecting the meter tails.)
I have recently qualified, though yet to start practising, as an electrician.
I have noticed, at my home, the tails from the (single phase) 100A mains cut out to the 100A rated meter, from the meter, to a 60A isolator and from the isolator to the antiquated fusebox are all 16mm. I have looked up on this forum and elsewhere about 16mm tails on 100A supplies, so I am fairly up to speed on the debate, but ...
- My mains cut out was upgraded in January 2015 (long, long before I ever thought of becoming an electrician) to a Henley Series 8 with a type II 100A fuse.
- I know the DNO’s last point of responsibility is the exit point of the cut out.
- The DNO (in my case Western Power) claims (maybe quite reasonably) not to be obliged to have to conform to IEE (and hence BS7671) regulations
This is my thinking: BS 7671 110.2 (i) excludes systems for the distribution of electricity to the public from 7671, but would not BS 7671 regulations still apply when reconnecting meter tails as these would be part of the domestic installation even if the cut out fuse was regarded as part of the distribution system? (NB at this point I am not saying necessarily that the 16mm tails would be a violation of BS7671, it’s more an academic question as to whether the person/organisation replacing the cut out is subject to IEE regulations when reconnecting the meter tails.)
- BS 7671 Table 4D1A provides no data on the current carrying capacity of 16mm Single-core 70°C Thermoplastic Insulated, Non-Armoured, Sheathed Cables (i.e. 16mm 6181Y meter tails) for Reference Method F (in free air) both touching and spaced by 1 diameter.
- I do find the odd reference from retailers to the current carrying capacity being 87A, such as this: 6181Y 16.0mm² Tails Brown 50M - Cut to Length - https://www.tlc-direct.co.uk/Products/CA16TBRslash50.html, but that is for Reference Method C, clipped direct.
- Western Power have a policy document (MI13A/8 to be precise!) which says that all main current carrying conductors should be a minimum of 16mm2 and a fuse of up to 100A will give adequate overload protection for this size of conductor. WPD do not publish this policy document for the public or electricians to see.
- Western Power say their policies are strictly regulated.
- However, on their website they do have a document (Company Directive SD5D/2: https://www.westernpower.co.uk/downloads/3347) which refers to 'Arrangements for LV Cut-Outs'. That, states “The service cable and the tails connected to the cut-out shall be rated at, or above, the cut-out fuse rating, taking account of the installation method.” This is dated February 2013, so almost two years before my cut out was upgraded.
- I have asked Western Power if they have any definitive data on the current carrying capacity of 16mm tails. They did not directly answer that query. All I got was a quote from their unpublished policy document stating 16mm tails conductors were permitted.