Hi people
Just starting to do the 17th edition course.
Trying to find in the book bs7671 , the answer to a very simple question. I believe that actually knowing the answer and where it is to be found in the book will help me pass the course.
Heres the question>>>>
A 230V circuit is protected by a 20A type B circuit-breaker to BS EN 60898. The minimum value of fault current to ensure compliance with maximum disconnection times is:
Don't need the answer just where can I find it in the 17th edition book. I've looked in part 4, the contents page the index. can't find the answer.
Any help or pi$$ taking gratefully recieved:D
Hi Mac
Thanks for your help
But table 41.1 is on page 46 of the 17th edition bs 7671 book and is for maximum disconnection times. I still cannot find it. I think I need a brain transplant.
After noting that required trip time is 0.4 secs from the afor mentioned table then go to Appendix 3 Time~current characteristics, go to page 249 run your finger along 0.4mS until you hit the 20A breaker curve; that will give you the minimum fault current to trip (100A)
Thank you notsosmart for pointing that out to me.
I now have learnt to pay attention to the appendices as well as the parts to look for the answers. I got into the flow of just looking at the part for that set of questions.
Thanks to you both for the input.
I was told to presume that the questions are in order of the parts. I think i might just rely on knowing which part to go to, to find the answer
My pleasure,
The thing to remember is that exam question setters try to be clever & mix things up so (as in the example you gave) a fairly straight forward question becomes a bit of pain to extrapolate exactly what & where to find the answer.
Good luck with the course & Exam.
Throw a few more example qustions at the forum its good to keep the grey matter churning;)
Essex
17th edition Can't find it in the book? help please.
ChristianG,
Notsosmart,