Would be grateful for comments on this one relating to a recently installed CU. It is a MK Sentry split load type. One group of circuits is protected by an 30 mA RCD rated at a current of 80A. Adding up the MCBs there are 112 amps worth on this one RCD.
My understanding (perhaps mistaken) is that this is incorrect. The maximum possible current should be less than 80A , no diversity. Would be grateful if anyone out there could comment, confirm or otherwise.
Thanks