Alright folks, I am studying for my 17th edition exam and I have come across a question in the pastpapers I am struggling with. Anyone who can point me in the right direction on how to calculate the answer would be much appreciated.
A single phase load of 13A is supplied via a 15A BS1316 fuse isning single-core 70 degree c thermoplastic copper cables installed to method 4 (reference method B). The rating factor for grouping is 0.7 and for ambient temperature is 0.87, and overload protection is to be provided. The minimum acceptable size cable will be?
a. 1mm sq
b. 1.5mm sq
c. 2.5mm sq
d. 4 mm sq
A single phase load of 13A is supplied via a 15A BS1316 fuse isning single-core 70 degree c thermoplastic copper cables installed to method 4 (reference method B). The rating factor for grouping is 0.7 and for ambient temperature is 0.87, and overload protection is to be provided. The minimum acceptable size cable will be?