E

Eric-George

Hi Guys,

Firstly, this is my own project and I have no 3ph supply in my own unit and have to take a supply from neighbors unit who has an old 3ph rewireable board with plenty of spare spaces.

I cant upgrade neighbors board and have to run a cable 35- 45m to supply a 18kw heater and fans.

My question is what size fuses do I need ??

The total current works out to be 43 amps with a 3.3% volt drop.

This gives me a minimum cable size of 6mm 4 core swa.

The question is . . . . . Do I try to source 45a fuse wire to cover the total current load or is the total current (43a) divided by the 3 phases making the fuse sizes smaller ???

Appreciate all your suggestions.
 
Not sure where you got that 43amps from as an 18kw load over 3 phase would be 26amps per phase

Malcolm, you may have just answered my question. I got the 43a from dividing power by voltage (18000 / 410). I'm sure there a square root of 3in the calculation that I've missed?

43/ sqrt 3 (1.73) = 26 !!

Telectrix - Fans and heater are all 1 unit with 3 ph supply.
 
think the way forward is to split the tails to the neighbour's DB, install a 40A 3 phase MCB to feed your installation, add a meter if required so neighbour can charge for what you use. 6mm SWA if it meets VD limits beats 3 rusty nails in his DB.
 

Reply to 18kw heater - 45m cable run - 3 phase - rewireable fuses. . . . Fuse size ???? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487
For a TN system neutral is deemed at earth potential.
Replies
6
Views
357

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top