Hi all,

I went out to a weekend call out where the customer had had a fluorecent tube and starter replaced. Apparently the light had shone brightly for a short time and then went out.

I opened up an outer piece of casing which revealed little more than a choc block. I tested for voltage and got constant readings of 18V LN and 10V LE (0V NE). There was no apparent means of openning up the lamp and not wanting to risk breaking an old fitting in the evening I am yet to look inside. fixed wiring (black insulated) seems to just reach the choc block from beneath the fitting with the white insulated wiring for the fitting on the other side.

Is there something basic I am missing here?
 
If it has a starter there must be a choke somewhere. With the tube out you should read mains voltage between one pin at one end and one at the other, and nothing on the other two that connect to the starter. Sounds like a duff choke, shorted turns will overrun the lamp.
 
18 volts l-n on the chockblock with incoming power? theres your problem, have a look whats up on the rest of the circuit.
if thats black insulation and its old you may have a VIR cable and its insulation may fall apart as soon as you disturb it.
 
18 volts l-n on the chockblock with incoming power? theres your problem, have a look whats up on the rest of the circuit.
if thats black insulation and its old you may have a VIR cable and its insulation may fall apart as soon as you disturb it.


Thanks both

the light is on the down light circuit which is happily populated by 240 fittings. The replaced starter and starter fitting is of standard type and the tube fitting has standard pins.

the black insulation of the conductors seems to be PVC, nothing crumbly about it.

the physical sequence of the components are:

main body of fitting
black insulated conductors
choc block giving 18v LN and 10v LE and positioned ~3 mm from main fitting
white insulated conductors looping back into the fitting

any further thoughts
 

Reply to 18v at fluorescent in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks davesparks. Looking at the diagram on the driver that's what I interpreted too, but I heard somewhere that the DALI system doesn't like...
Replies
2
Views
553
  • Question
It sounds like the original meter was reading incorrectly and octopus aren't keen to admit this as they would probably have to refund you. I...
Replies
1
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top