ianbrookes

any ideas would be gratefully accepted.

went to a job today. no upstairs lighting at all, did various tests, 240v at the CU, 195v at several of the fittings.

lighting is loop in ceiling roses/fittings, switches are line in and swl, mixture of dimmers and switches.

to bathroom fans on isolators, pullcords in bathrooms to operate lights (and assume switch fans - I couldn't test, not enough voltage)

circuit is small in length and number of fittings.

has anyone come across this before ?
 
242v at output of fuse in CU L-N
195V at fittings L-N
even the first fitting does not work
there is a two-way switch in the downstairs, no neutrals, just line conductors - this doesn't work for the landing light either

it must be a bad neutral somewhere, the cable is in really good shape, no signs of any degradation (what I can see anyway)

thanks to all
 
went to a job today. no upstairs lighting at all, did various tests, 240v at the CU, 195v at several of the fittings.

When you say "no upstairs lighting at all", do you mean that there was not enough current to light a lamp? If you are measuring this "195V" with no load on the circuit, then there's probably a break in the supply and the voltage you are measuring is a phantom or induced voltage.

What is the voltage with, say, an ordinary GLS lamp across the supply? If zero, or close, then it's a break rather than a resistive fault.
 
242v at output of fuse in CU L-N
195V at fittings L-N
even the first fitting does not work
there is a two-way switch in the downstairs, no neutrals, just line conductors - this doesn't work for the landing light either

it must be a bad neutral somewhere, the cable is in really good shape, no signs of any degradation (what I can see anyway)

thanks to all

Well, that will tell you where to start looking for the fault on this circuit then, won't it! ...lol!!
 
242v at output of fuse in CU L-N
195V at fittings L-N
even the first fitting does not work
there is a two-way switch in the downstairs, no neutrals, just line conductors - this doesn't work for the landing light either

it must be a bad neutral somewhere, the cable is in really good shape, no signs of any degradation (what I can see anyway)

thanks to all

Did you test for voltage between L-E and if you did what voltage was present?
 
Whats going on?!? Going to a fault with 50 volts lost and not testing between all conductors and then no IR or continuity tests?

Were you not taught this in your apprenticeship? Fault finding and rectification, spent about half my 3rd year doing it and still struggle with faults in the first few years after that.

Sounds like a break on the feed from the CU and first pendant, I try a long lead method on each conductor back to the CU and see if results are consistent between L-N and slightly higher on E if its wired in twin. If not its hammer out time!
 

Reply to 195v on a domestic lighting circuit in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Question
Interesting document thanks. But it neglects the half-wave rectification, and also totally neglects the effect of the coil inductance when...
2
Replies
31
Views
2K
Thanks will give that a try in a little while Cheers Writing to say thank you very much for that advice, its worked! Really appreciate the help
Replies
6
Views
760
You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
925
Hi James, Many thanks for your response and suggestions. The only reservation I have about leaving things as they are and making a contribution...
Replies
2
Views
615
SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks