I have just moved into a 3 bed end-of-terrace built in 1969 that was supposed to have still-functional electric underfloor heating in the concrete.
An electrician said it wasn't working and disconnected it (removed the thermostats and cut the cables running to the consumer unit, even though I did not specifically request this).
In his report he based this judgement on the fact that the 3 underfloor heating circuits supplying the thermostats all gave 0 Mohms insulation resistance readings at 250v (between L-E, L-N and N-E. He went on to explain: "Upon further inspection, parts of 2 of the circuits (the first legs of the circuits running from the consumer unit to the stats) appear to have been rewired approximately 25 years ago with a newer pvc insulated cable, replacing the original mineral insulated cable that would have been installed when the house was built some 40+ years ago (likely a necessary repair due to corrosion over time of the original mineral insulated cables due to being buried in concrete). My conclusion is that the original mineral insulated cabling still running through all 3 circuits, to most parts of the underfloor heating, has corroded to the point that it can no longer correctly conduct electricity. The same insulation resistance readings were obtained from each of the stat locations on the original mineral insulated cables. No testing was carried out above 250v as individual disconnection of the heating mats was not possible."
When I asked the electrician if there was a way of re-testing it now that he'd removed the thermostats, he said that it could be by knocking through the plaster where the thermostats were and testing the readings on the wires. Another electrician did this for me and got normal resistance readings. He said that the original electrician should have tested for resistance and not insulation resistance, as underfloor heating mats will always give a 0 Mohm insulation resistance reading.
When I went back to the original electrician with this he said: "I carried out an insulation resistance test of three underfloor heating circuits at the consumer unit with the thermostats in the satisfied position (turned down/off) which breaks the line conductor. Finding a short circuit between Line/CPC, Line/Neutral and Neutral/CPC I concluded that the cabling running to the underfloor heating thermostats was defective. The only time you would expect a result of 0 Mohms is if you were to carry out an insulation resistance test on the underfloor mats themselves, which is not a mandatory part of the EICR. If you were to carry out an insulation resistance test on the underfloor mats themselves you would expect a reading of 0 Mohms between Line/Neutral ONLY, NOT between Line/CPC or Neutral/CPC. An EICR is only concerned with the installation wiring NOT the local accessory wiring. I believe the resistance readings you have informed me of were obtained locally by testing for resistance NOT insulation resistance of the underfloor mats themselves."
The original electrician at first implied it wasn't worthwhile replacing the underfloor heating as the mats were in the concrete and be impossible to reach. However, he now seems to be saying that since we said we weren't going to use the underfloor heating anyway, rather than any rewiring to it disconnection would be the cheapest option.
I am in the difficult situation of having heard two different things from two different electricians. I want to get the underfloor heating fixed if possible. My questions are:
1) Can anyone hazard a guess on whether it's actually broken or not from the above?
2) Is it possible to rewire it if so in order to make it functional? The second electrician quoted ÂŁ720 to chase new cables to it. Would that fix it and is that even possible if the mats are in the concrete?
The property has no gas supply and I will probably install fan-assisted storage heaters in any case, but I would like to salvage the underfloor heating since I've heard the in-concrete type installed in the 60s was very effective as a heat store.
Thanks so much in advance.
An electrician said it wasn't working and disconnected it (removed the thermostats and cut the cables running to the consumer unit, even though I did not specifically request this).
In his report he based this judgement on the fact that the 3 underfloor heating circuits supplying the thermostats all gave 0 Mohms insulation resistance readings at 250v (between L-E, L-N and N-E. He went on to explain: "Upon further inspection, parts of 2 of the circuits (the first legs of the circuits running from the consumer unit to the stats) appear to have been rewired approximately 25 years ago with a newer pvc insulated cable, replacing the original mineral insulated cable that would have been installed when the house was built some 40+ years ago (likely a necessary repair due to corrosion over time of the original mineral insulated cables due to being buried in concrete). My conclusion is that the original mineral insulated cabling still running through all 3 circuits, to most parts of the underfloor heating, has corroded to the point that it can no longer correctly conduct electricity. The same insulation resistance readings were obtained from each of the stat locations on the original mineral insulated cables. No testing was carried out above 250v as individual disconnection of the heating mats was not possible."
When I asked the electrician if there was a way of re-testing it now that he'd removed the thermostats, he said that it could be by knocking through the plaster where the thermostats were and testing the readings on the wires. Another electrician did this for me and got normal resistance readings. He said that the original electrician should have tested for resistance and not insulation resistance, as underfloor heating mats will always give a 0 Mohm insulation resistance reading.
When I went back to the original electrician with this he said: "I carried out an insulation resistance test of three underfloor heating circuits at the consumer unit with the thermostats in the satisfied position (turned down/off) which breaks the line conductor. Finding a short circuit between Line/CPC, Line/Neutral and Neutral/CPC I concluded that the cabling running to the underfloor heating thermostats was defective. The only time you would expect a result of 0 Mohms is if you were to carry out an insulation resistance test on the underfloor mats themselves, which is not a mandatory part of the EICR. If you were to carry out an insulation resistance test on the underfloor mats themselves you would expect a reading of 0 Mohms between Line/Neutral ONLY, NOT between Line/CPC or Neutral/CPC. An EICR is only concerned with the installation wiring NOT the local accessory wiring. I believe the resistance readings you have informed me of were obtained locally by testing for resistance NOT insulation resistance of the underfloor mats themselves."
The original electrician at first implied it wasn't worthwhile replacing the underfloor heating as the mats were in the concrete and be impossible to reach. However, he now seems to be saying that since we said we weren't going to use the underfloor heating anyway, rather than any rewiring to it disconnection would be the cheapest option.
I am in the difficult situation of having heard two different things from two different electricians. I want to get the underfloor heating fixed if possible. My questions are:
1) Can anyone hazard a guess on whether it's actually broken or not from the above?
2) Is it possible to rewire it if so in order to make it functional? The second electrician quoted ÂŁ720 to chase new cables to it. Would that fix it and is that even possible if the mats are in the concrete?
The property has no gas supply and I will probably install fan-assisted storage heaters in any case, but I would like to salvage the underfloor heating since I've heard the in-concrete type installed in the 60s was very effective as a heat store.
Thanks so much in advance.