Hi Guys,

This is the second time I've come across this on an EICR, but with slightly different circumstances.
It has made me ponder if my previous code, and if my current idea for coding is correct or not.

Basically someone has bodged an extra single phase supply off the incomer side of a 3 Phase DB Isolator. To me this is bad workmanship and people who do it should recieve a slap..! Surprisingly, they managed to get it to fit without trimming strands off.

Previously scenario it was protected by an MCCB, I coded it a C3, as if the phase it was on tripped on over-current, it would trip the whole MCCB Making the motors, heaters and other accessories on the 3PH db safe. So to me, a C3 seemed legit. Wasn't sure what BS7671 number to put on it.

In this scenario it's protected by a BS88 3PH Switch fuse.
Now i'm thinking this time round, it should be a C2, as if it we're to blow the fuse on OC, the machinery on the rest of the board could go into OC.
Once again, no idea on what reg no to put on it.

Anyone got any feedback or had experience with this?

Cheers,
Steve
 
It doesn't sit right with me. what I suppose you have to assess is taking diversity into account are the three phases reasonable balanced and that one of the phases is now overloaded. If a circuit breaker is used all three phases are disconnected if a fault/O.L. happens however a fuse could blow under these circumstances even if the piggyback load was not there
 
Yes, it's not so much about how many phases each DB has, or whether the shared submain has linked OCPD, but whether the piggyback load pushes the submain beyond design current. If not, e.g. that phase on the TP+N DB is suitably light, then the problem is an organisational one of the shared submain rather than one of loading. If that phase is now too heavily loaded, it's like any other overloaded DB.

TP loads should be resilient to loss of a phase as this is still a common occurrence despite many circuits having linked OCPD. Supply faults are often one phase down, or one company fuse out. Some are not as well protected as they should be though.
 

Reply to 1ph DB Piggy backed off 3ph DB Before Isolator. - EICR in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
281
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
791

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top