M

Maff

I have just set up a PV installation company and we are embarking on our first job and MCS accr. In order to maximise the yeild of the array for the given roof area we are going to install 15 modules in 3 parallel strings conected to an SMA SB-3000 TL inverter, the thing is on the 2399 course array frame earthing was a bit vague, my research says we will need a rod and RCD protection, does anybody have any advice on distances from property etc and will I have to go and buy an electrode tester?
 
SMA TL will require a rod on TN-C-S, and why not use method 2 to check the suitability of the rod.....
 
Been discussed many times, however there dosent seem to be a specific regulation covering it. Most courses recomend a minimum 300mm clear zone from the roof edge. This seems to be the acceptable distance that reduces wind loading/lift implications
 
What about 300 up to the ridge, 600 at each side and 200 at the bottom, would that be pushing it?
 
You need to get it right on your 1st install and keep it there. 200mm is pushing it IMHO
 
The risk of 200m at the bottom is:
- wind catching the edge if it is in an exposed location
- rainwater running down the panel and overshooting the gutter

It is not a definite no-no, but I would be wary of going so close on your first install or until you have the experience to make a sound judgement of actual conditions on site. You would need to be able to explain to your assessor why you did it that way.

Regards
Bruce
 
We being the cautious types like to go for 450mm if we can, we'll only squeeze down to 300 on very few occassions, and then we nearly always decrease the bracket spacing (doubling up effectively) in the bottom corners. All depends exactly what the wind uplift calcs come out at.

Don't forget you'll need to show your structural calcs etc for the MCS assesment.
 
cheers , all being taken on board.I am doing a CU change at the same timeand installing a split load board, as its a TL inverter can I put the 20A mcb on the protected side or does it have to be its own bespoke RCD on the unprotected side, prob more stupid questions to come, we have gone for the smaller array which has 600 clearance all round to be on the safe side at the expense of 0.6KW.
 

Reply to the thread, titled "1st install advice" which is posted in Solar PV Forum | Solar Panels Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top