Hi All,
I have just been to look at my first potential job since getting 17th Ed and Dom Installer qualificaion.
I need to install 2 outside lights and a garage ring main. The set up is a TT installation with a split load Hager board. My concerns and questions are as follows;
1) There is an rcd protecting the sockets, power shower and cooker but the lighting circuits have no rcd protection at all, the main switch is a straight 100 A DP. These should have rcd potection regardless for a TT, I would like some advice on the best way to resolve this, I though of adding a 63 or 80 A rcd and then moving the mcb's for the sockets and lighting to give some discrimination or adding a new circuit on a RCBO and letting the customer know the issue with the rcd protection.
2) The CU is on the outside wall in the garage so I intended to run the cable from the consumer unit up the garage wall and then out through the building in T & E and then to a box, I am not sure what is the best cable to use for the run to the 2 lights given the temperatures we get during the winter and the UV light degradation? (or should I use a different cable for the complete run back to the cu)
3) For the garage ring I will be installing in conduit for additional protection, what is the view generally on cable runs in garages regarding additional protection? i am thinking of s/w drops and boiler feeds etc.
I will be using this work for my assessment so your guidance would be much appreciated.
Thanks,
Scotty
I have just been to look at my first potential job since getting 17th Ed and Dom Installer qualificaion.
I need to install 2 outside lights and a garage ring main. The set up is a TT installation with a split load Hager board. My concerns and questions are as follows;
1) There is an rcd protecting the sockets, power shower and cooker but the lighting circuits have no rcd protection at all, the main switch is a straight 100 A DP. These should have rcd potection regardless for a TT, I would like some advice on the best way to resolve this, I though of adding a 63 or 80 A rcd and then moving the mcb's for the sockets and lighting to give some discrimination or adding a new circuit on a RCBO and letting the customer know the issue with the rcd protection.
2) The CU is on the outside wall in the garage so I intended to run the cable from the consumer unit up the garage wall and then out through the building in T & E and then to a box, I am not sure what is the best cable to use for the run to the 2 lights given the temperatures we get during the winter and the UV light degradation? (or should I use a different cable for the complete run back to the cu)
3) For the garage ring I will be installing in conduit for additional protection, what is the view generally on cable runs in garages regarding additional protection? i am thinking of s/w drops and boiler feeds etc.
I will be using this work for my assessment so your guidance would be much appreciated.
Thanks,
Scotty