i came a cross a 16mm two core cable today and they want an other small supply taking off if. can i still use it? as i got told, you can only use the armor for an earth if the cable size is no bigger than a 6mm. i was thinking can i install an earth rod and RCD's to get round this problem
thanks​
 
i came a cross a 16mm two core cable today and they want an other small supply taking off if. can i still use it? as i got told, you can only use the armor for an earth if the cable size is no bigger than a 6mm. i was thinking can i install an earth rod and RCD's to get round this problem
thanks​

I think you have been misinformed. The SWA of a 16mm 2 core should be fine to use as a CPC.


Sent from my iPhone using Tapatalk
 
For a 16mm^2 armoured cable the minimum required CSA of armour for use as a circuit protective conductor is 49.74mm^2

A bs 5467 or bs 6724 (XLPE) 2 core 16mm^2 SWA cable has 42mm^2 of armour so would be unsuitable for use as a circuit protective conductor

A BS 6346 2 (Low Smoke Zero Halogen) core 16mm^2 SWA cable has 46mm^2 of armour so would also be unsuitable as a circuit protective conductor
 
CSA also depends on protective device and disconnection time - see Adiabatic Equation section 543.1 of 17th Edition, that will give you a more accurate calculation of what the minimum CSA of the armour needs to be.
 
CSA also depends on protective device and disconnection time - see Adiabatic Equation section 543.1 of 17th Edition, that will give you a more accurate calculation of what the minimum CSA of the armour needs to be.

Good man! :)

There's often a bit more to it than 'it doesn't comply'
 
For a 16mm^2 armoured cable the minimum required CSA of armour for use as a circuit protective conductor is 49.74mm^2

A bs 5467 or bs 6724 (XLPE) 2 core 16mm^2 SWA cable has 42mm^2 of armour so would be unsuitable for use as a circuit protective conductor

A BS 6346 2 (Low Smoke Zero Halogen) core 16mm^2 SWA cable has 46mm^2 of armour so would also be unsuitable as a circuit protective conductor

Where did you get 49.74 from ?
 
The PDF in post #3 is copied from Guidance Note 1 by The IEE, and supports the use of the armour as a CPC where it determines it to be large enough.

Of the 2 types of SWA (PVC & XLPE), only one of the 16mm 2 core cables is suitable for use as a CPC so you need to be careful if you do decide to use the armour about which type you have.
 
If you read the ECA book - Guide To the Wiring Regulations, they basically say that most SWA cables don't need an external cpc, and say that the SWA is sufficient. If I remember correctly anything up to 400mm would be Ok and the 120mm size is marginal and should be OK unless its used at full current carrying capacity.

Again if you use the Adiabatic equation that should prove it!
 
If you have an SWA cable where the armour falls short of requirements to be used as CPC can you just make up the difference by having the armour combined with a small external earth wire terminated on an earth ring with the SWA gland or must you use either the armour or an extraneous earth wire alone.
 
If you have an SWA cable where the armour falls short of requirements to be used as CPC can you just make up the difference by having the armour combined with a small external earth wire terminated on an earth ring with the SWA gland or must you use either the armour or an extraneous earth wire alone.

The additional cpc must be sized as if it alone was the cpc. Guidance Note 8
 
from the nic technical manual and if someone can tell me how to insert a PDF file I will attach it

Did you read the correct column as the figure I have is different ?

To post a pdf when you reply to a post, scroll down to MANAGE ATTACHMENTS and click this then browse on your hard drive to the PDF file then click UPLOAD
 
QUOTE=Canoeboy;208748]Did you read the correct column as the figure I have is different ?

I may have missed something but I hope the attached is correct and answers your question.


View attachment 3307

You haven't missed anything as such but the table only indicates a non-compliance with table 54.7 whereby you can then use the adiabatic equation to size your cpc which invariably results in a lower required CSA by calculation.
 
You haven't missed anything as such but the table only indicates a non-compliance with table 54.7 whereby you can then use the adiabatic equation to size your cpc which invariably results in a lower required CSA by calculation.

Yes you can use the adiabatic equation but I was asked where my figure of 49.74 came from. The table will not give the most economical solution in all cases but it is an easy reference chart and always works on the side of caution. This means that at least your CPC will not be undersized. You would still be advised to use the equation to check though.
 

Reply to 2 core armored cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K
Sounds more positive.
Replies
8
Views
472
dreadful, I couldn't sleep at night after that install, it may just about pass but the quality of work is substandard IMO
Replies
4
Views
472
  • Question
Issue is certain sizes of cable may theoretically be okay but upon the proper testing when it’s commissioned things like a thing may not test out...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks