2 Gang UK Socket - Capable of 26Amp or Only 13Amp? | on ElectriciansForums

Discuss 2 Gang UK Socket - Capable of 26Amp or Only 13Amp? in the UK Electrical Forum area at ElectriciansForums.net

Joined
Apr 1, 2022
Messages
17
Reaction score
1
Location
London
Its common to read in literature and textbook, that providing we use an adequate twin earth rated cable, a UK Double socket is capable of 26Amp, however whenever I browse actual catalogues to buy, all I can find are 13Amp rated.

Example below...

Is this because its implied 13Amp per plug?

In my setup I need to run continuously 25Amps for my bitcoin miner, I intended to run a 2 gang socket via a Radial setup with 4mm twin & earth... as its easier not having to loop back ring circuit.




[ElectriciansForums.net] 2 Gang UK Socket - Capable of 26Amp or Only 13Amp?
 
Last edited:
Double sockets are typically rated at 20A overall, 13A max per socket. If you really do want 2 * 13A as you might in a kitchen with high load appliances then you are better going for two single 13A sockets.

If you have a single load that is 25A then you need something like the 32A 'commando' sockets & plugs (round blue things).

However I seriously doubt that bitcoin mining is a good idea in economics now as the cost of energy is so high and the rewards getting lower.
 
As above, 20A per double total although IMO one gets much more trouble from the individual sockets barely handling 13A (partly also due to the plugs) than from the total load exceeding 20A. The only parts carrying the total load are simple metal strips and screw terminals, whereas the heat is mainly generated in the socket contacts and switches which are individual to the two sides. Also as above, best to use two single sockets to supply 2 x 13A.

We used to have background heating for one of our warehouses provided by mining, when returns were higher, ASIC miners were new and ahead of the curve, and electricity was cheaper. By the time I had set a similar system up at home, the economics were less favourable. I don't know how the figures stack up these days at all.
 

Reply to 2 Gang UK Socket - Capable of 26Amp or Only 13Amp? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top